A client asked me to add two sockets in their bedroom

I took power from two sockets in the lounge which is behind the bedroom wall.

I ran a cable out of each socket for the new socket

The problem is it now is tripping the RCD and blowing the old Existing sockets and light switches

But the new sockets I added still work fine

The old existing sockets and switche are blown and unusable

When I try to reset the RCD It pops and Sparks down

Any idea to why this is happending
 
if the old sockets were on a ring, and one leg has popped out... the new sockets, being connected will still work, but theres maybe another floating live touching the metal back box.

can you take photos of the back of the sockets? there might be something obvious to us that you havent seen
 
if the old sockets were on a ring, and one leg has popped out... the new sockets, being connected will still work, but theres maybe another floating live touching the metal back box.

can you take photos of the back of the sockets? there might be something obvious to us that you havent seen
The thing is the client phone back saying there’s no power and the RCD is popping down and sparking so I went back same night, and opened up the sockets I touched the connections were fine the socket sparked and popped while the socket was open so no loose lives
 

Attachments

  • [ElectriciansForums.net] Blowing sockets and popping RCD
    54001265-E860-4A32-9457-62D59B700C4E.jpeg
    370 KB · Views: 69
no the actual sockets sparked and blew in front of me
The mcb never tripped once only the RCD

On the assumption you're trained and experienced, what does that tell you ?

so I went back same night, and opened up the sockets I touched, the connections were fine, the socket sparked and popped while the socket was open so no loose lives

Did you leave the socket sparking and popping when you left or have you isolated it / them?
 

Reply to Blowing sockets and popping RCD in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
429
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
677
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
704
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top