Hi all

Been asked to quote for a board change. Had a quick look round the place and discovered lighting circuit has no earth. Where do I stand on this?

Current board is 3036s and will be replacing with rcbos as wiring is quite old. Will also be bonding the gas and water from 4mm to 10mm.
 
lighting circuit is ok as long as it doesn't have any class 1 fittings or switches on it reconnect it to new consumer unit and make note on certificate

That's what I think as well, but I notice that the Best Practice Guide is a little more flexible than that if the customer refuses to replace Class I fittings or rewire the circuit / install a protective conductor, maybe a little too flexible?
 
The esc cu guide actually allows you to fit a new consumer unit even with metal unearthed fittings

as long as they are not outside or within reach of any extraneous conductive parts

but you must perform an IR test between the live terminal and the meatallic casing of the fitting i think if memory serves correct?
 
The esc cu guide actually allows you to fit a new consumer unit even with metal unearthed fittings as long as they are not outside or within reach of any extraneous conductive parts
The ESC is not in a position to allow or forbid anyone to do anything. It is a guide.

but you must perform an IR test between the live terminal and the metallic casing of the fitting i think if memory serves correct?
Are you sure? What would that prove, other than it was not live when you tested it?
 
The esc cu guide actually allows you to fit a new consumer unit even with metal unearthed fittings

as long as they are not outside or within reach of any extraneous conductive parts

but you must perform an IR test between the live terminal and the meatallic casing of the fitting i think if memory serves correct?

Would recommend if you post somthing like this, that backing it up with a link to the approprate documentation would help.
 

Reply to Board change with no cpc on lighting in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
321
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
848
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
971

Similar threads

Promised a photo…. Remember, this was working…. And they managed to move in without hitting it…
    • Like
Replies
4
Views
359

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top