uksparks
-
Hi,
Went to look at a board change this morning, all seems fine, nothing untoward, only thing was on the downstairs ring the CPC continuity was higher than I would have liked.
r1 = 0.39
rn = 0.41
r2 = 1.44
I was half expecting around 0.75 ish, how far over the expected do you accept without investigation? I would imagine its probably just a poor connection in a socket somewhere. Usually I would look and see if i tighten them all up a bit, but would it be acceptable to change the board would you say without doing anything and just making a note of it?
The Zs on all sockets were fine, just the continuity on the ring that's all. So really just wondering if you have an upper limit as to saying "yeah that will do" before you look into it.
Where do you draw the line of acceptable?
Cheers,
Went to look at a board change this morning, all seems fine, nothing untoward, only thing was on the downstairs ring the CPC continuity was higher than I would have liked.
r1 = 0.39
rn = 0.41
r2 = 1.44
I was half expecting around 0.75 ish, how far over the expected do you accept without investigation? I would imagine its probably just a poor connection in a socket somewhere. Usually I would look and see if i tighten them all up a bit, but would it be acceptable to change the board would you say without doing anything and just making a note of it?
The Zs on all sockets were fine, just the continuity on the ring that's all. So really just wondering if you have an upper limit as to saying "yeah that will do" before you look into it.
Where do you draw the line of acceptable?
Cheers,