Boiler emergency e-stop | Page 3 | on ElectriciansForums

Discuss Boiler emergency e-stop in the Commercial Electrical Advice area at ElectriciansForums.net

I re-iterate the OP is in the USA.
CE markings and BS, EN, standards therefore don't mean a thing.

The USA have their own standards that they have to work to, so the principle still applies.
 
As an overview here to simplify it a bit, you have to treat an E-Stop actuator like a normal stop button, on it's own it is not an E-Stop even it it complies with the standards by design, it is only an E-Stop when part of an E-Stop system that meets relevant standards.
It is like sticking a Lamborghini badge on a Fiesta, the badge does not change the car to a Lamborghini and on its own the badge is not a Lamborghini even if it is made for one, the same applies to the various stop actuators that comply to be used as E-Stops.
 
As an overview here to simplify it a bit, you have to treat an E-Stop actuator like a normal stop button, on it's own it is not an E-Stop even it it complies with the standards by design, it is only an E-Stop when part of an E-Stop system that meets relevant standards.
It is like sticking a Lamborghini badge on a Fiesta, the badge does not change the car to a Lamborghini and on its own the badge is not a Lamborghini even if it is made for one, the same applies the various stop actuators that comply to be used as E-Stops.
I think you're right about that. They are using the word e-stop wrong. They just want something to kill power to the boiler if there's an emergency or issue
 
I re-iterate the OP is in the USA.
CE markings and BS, EN, standards therefore don't mean a thing.
I didn't see that stated anywhere. ?‍♂️
The USA are catching up with the ISO & IEC standards requirements as they are members of both organisations.
They are just a bit slower than the rest of the world because of the difference in the way they blame people and mandate PPE rather than addressing the real hazards.
Also their equipment design is about 20 years behind the world that has embraced the IEC standards, having assessed both, the US equipment is positively dange in comparison to equipment to base IEC requirements.
Almost all BS & EN standards are derived from ISO & IEC source document, some are identical, and if North America was not so stuck in its ways and arrogant about their so called supremacy, they would accept the standards they had a hand in writing, and save millions in currency and massive global resources.
Plus some of the documents I have quoted are ISO standards so the USA are bound to implement them in the same way the UK has to implement IEC 60364.
The control philosophy in the US is aligning and the intent is similar.
 
I didn't see that stated anywhere. ?‍♂️
The USA are catching up with the ISO & IEC standards requirements as they are members of both organisations.
They are just a bit slower than the rest of the world because of the difference in the way they blame people and mandate PPE rather than addressing the real hazards.
Also their equipment design is about 20 years behind the world that has embraced the IEC standards, having assessed both, the US equipment is positively dange in comparison to equipment to base IEC requirements.
Almost all BS & EN standards are derived from ISO & IEC source document, some are identical, and if North America was not so stuck in its ways and arrogant about their so called supremacy, they would accept the standards they had a hand in writing, and save millions in currency and massive global resources.
Plus some of the documents I have quoted are ISO standards so the USA are bound to implement them in the same way the UK has to implement IEC 60364.
The control philosophy in the US is aligning and the intent is similar.
They do have NFPA 79 which would be their regional variant of the ISO standard
 

Reply to Boiler emergency e-stop in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
706
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

So much for trying to steer this back on track.
2 3
Replies
31
Views
982
Outside socket… ok. But you say the fcu for boiler is beside the outside socket… is the boiler outside too? FCU’s have an IN and an OUT… the OUT...
Replies
2
Views
217

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top