Hi...
I think I know the answer to this question but just wanted to hear what others said..
I'm upgrading a CCU and as part of the job I have done an inspection of the current installation which was a diy job. I don't think the owner was qualified but they have done quite a professional job and 'generally' pay gogod note to regs and safety etc.
However, there is no earthing to gas and water. I queried this with the owner. All water pipes are plastic but they have connected the gas pipe using a 10mm cable to copper heating pipes which are then eventually bonded to the ring main so effectively going back to the CCU via a 1.5mm earth. These connections are inaccessible.
I know this should be a 10mm straight to th CCU and will advise as such but what code would this be. Presumably it is then up to the owner. Would this be put as an advisory note on the certificate.
Also the Ze was super low at 0.06. Its a TT system with the Earth also connected to a lead water pipe in the garden
Any thoughts
I think I know the answer to this question but just wanted to hear what others said..
I'm upgrading a CCU and as part of the job I have done an inspection of the current installation which was a diy job. I don't think the owner was qualified but they have done quite a professional job and 'generally' pay gogod note to regs and safety etc.
However, there is no earthing to gas and water. I queried this with the owner. All water pipes are plastic but they have connected the gas pipe using a 10mm cable to copper heating pipes which are then eventually bonded to the ring main so effectively going back to the CCU via a 1.5mm earth. These connections are inaccessible.
I know this should be a 10mm straight to th CCU and will advise as such but what code would this be. Presumably it is then up to the owner. Would this be put as an advisory note on the certificate.
Also the Ze was super low at 0.06. Its a TT system with the Earth also connected to a lead water pipe in the garden
Any thoughts