Agreed mate. With separate buildings if you come along after build (and 1st/2nd fix electrics) and do a test you'll find a degree of continuity (IE low(ish) resistance ... because of the bonding). If you do it during construction (once the concrete has gone off) you'll find the resistance so high it ain't worth considering.
Warehouses are a whole different ball game as, as you mention, they often share some common conductive structure (same with office blocks).
In reality, I guess, the risk is only (potentially) marginally worse than any 3 phase fault, where phases are used individually (IE fault on one phase appearing physically close to another phases line). The risk then is that the cpc (on one phase) can now be in physical proximity to another phase (not sure I'd wanna be there).
Warehouses are a whole different ball game as, as you mention, they often share some common conductive structure (same with office blocks).
In reality, I guess, the risk is only (potentially) marginally worse than any 3 phase fault, where phases are used individually (IE fault on one phase appearing physically close to another phases line). The risk then is that the cpc (on one phase) can now be in physical proximity to another phase (not sure I'd wanna be there).