hi. Question re bonding a metal where cold comes in as metal pipe ground into house. So cold will be bonded where service comes in. Read article in wiring matters 2019 about changes for part 18. Example given of faulty kettle where fault to earth exists at kettle, some one touches kettle earth and metal tap, pipe should be same so neggligeable difference exhists and no shock. Just made me think for a bit...
Questions...
Why didn’t the fuse or circuit protective device operate leaving no touch voltage?
I assume above is because current not high enough to rupture, leaving a potential high enough to kill but not high enough to damage cable- assumes rcd not used... which is wrong in itself given the example, but let’s go by their example.
So really when we are bonding like this aren’t we suplimenting the supplied earth into the building with the general mass of earth and not the other way. round? For the example above to be dangerous the General Mass of Earth has to be of an impedance lower than the earth connected to the kettle. Otherwise the fault current would not flow with no touch voltage.
So this means then that GME is lower than supplied cable and when you do you EFLI testing you should disconnect all bonds, otherwise the reading will include a supply pipe as an earth path that could change if it is converted to plastic which could then mean the overall ZS is increased, increasing disconnection times.
Thoughts?
Questions...
Why didn’t the fuse or circuit protective device operate leaving no touch voltage?
I assume above is because current not high enough to rupture, leaving a potential high enough to kill but not high enough to damage cable- assumes rcd not used... which is wrong in itself given the example, but let’s go by their example.
So really when we are bonding like this aren’t we suplimenting the supplied earth into the building with the general mass of earth and not the other way. round? For the example above to be dangerous the General Mass of Earth has to be of an impedance lower than the earth connected to the kettle. Otherwise the fault current would not flow with no touch voltage.
So this means then that GME is lower than supplied cable and when you do you EFLI testing you should disconnect all bonds, otherwise the reading will include a supply pipe as an earth path that could change if it is converted to plastic which could then mean the overall ZS is increased, increasing disconnection times.
Thoughts?