hi. Question re bonding a metal where cold comes in as metal pipe ground into house. So cold will be bonded where service comes in. Read article in wiring matters 2019 about changes for part 18. Example given of faulty kettle where fault to earth exists at kettle, some one touches kettle earth and metal tap, pipe should be same so neggligeable difference exhists and no shock. Just made me think for a bit...

Questions...

Why didn’t the fuse or circuit protective device operate leaving no touch voltage?
I assume above is because current not high enough to rupture, leaving a potential high enough to kill but not high enough to damage cable- assumes rcd not used... which is wrong in itself given the example, but let’s go by their example.

So really when we are bonding like this aren’t we suplimenting the supplied earth into the building with the general mass of earth and not the other way. round? For the example above to be dangerous the General Mass of Earth has to be of an impedance lower than the earth connected to the kettle. Otherwise the fault current would not flow with no touch voltage.

So this means then that GME is lower than supplied cable and when you do you EFLI testing you should disconnect all bonds, otherwise the reading will include a supply pipe as an earth path that could change if it is converted to plastic which could then mean the overall ZS is increased, increasing disconnection times.

Thoughts?
 
the purpose of main bonding is to raise the potential of extraneous metalwork ( e.g. water pipes) to the 230V for the duration of the fault current. i.e. until the appropriate OCPD reacts.
 
the purpose of main bonding is to raise the potential of extraneous metalwork ( e.g. water pipes) to the 230V for the duration of the fault current. i.e. until the appropriate OCPD reacts.
That's one effect but the high level purpose is to create an equipotential zone which is basically preventing any potentially accessible conductive item introducing a different (from the installation earth) potential into the zone.
 
That's one effect but the high level purpose is to create an equipotential zone which is basically preventing any potentially accessible conductive item introducing a different (from the installation earth) potential into the zone.
agreed. both exposed conductive parts and extraneous parts are equipotential, so when an exposed part rises in voltage due to a fault, the extraneous parts rise the same.
 
What happens when the tap and bonding conductor has a resistance lower than the R2 of the socket circuit the kettle is plugged into?
then you hope that the touch voltage is <50V.
 
What happens when the tap and bonding conductor has a resistance lower than the R2 of the socket circuit the kettle is plugged into?
the fault disconnection time would be <400ms so it's deemed to be OK for that time.
But you are spot on and you illustrate exactly why supplementary bonding is essential in bathrooms - to remove the resistance between MET and the appliance CPC termination.
The only way around that is to have RCD protection on all circuits serving the bathroom which is a requirement for new installs anyway hence supplementary bonding going the way of the dodo.
 
the fault disconnection time would be <400ms so it's deemed to be OK for that time.
But you are spot on and you illustrate exactly why supplementary bonding is essential in bathrooms - to remove the resistance between MET and the appliance CPC termination.
The only way around that is to have RCD protection on all circuits serving the bathroom which is a requirement for new installs anyway hence supplementary bonding going the way of the dodo.
How does that work if for instance the fault current comes into the location via the pipework?
 

Reply to Bonding Extraneous Conductive Parts in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
971
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K
Was there any toast to go with the beans? Just joking I think that you ment beams and not beans I am dyslexic and simple mistakes tend to jump out...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top