Hi Guys
Doing an EICR of a property.
The client has an outbuilding with gas and water supplies. It has it's own CU fed from the main CU in the house.
The water is bonded but the gas is not.
The water supply is underground from the house in plastic and then changes to copper which is bonded.

The gas supply comes from the house in an underground copper pipe linked to the gas pipes in the house. So, electrically, it would be subject to the bonding in the house.
But does this negate the need to bond it in the outbuilding?

Looking forward to wise words!

Cheers
Pete:confused:
 
Last edited by a moderator:
Well when I went to school plastic did not make a good material for conducting electricity.

Read post #26!! I know the plastic pipe is not conductive ffs. I am talking with regard to the copper installation in the outbuilding. We know nothing about it from the OP's opening post so you cannot possibly know if it is extraneous or not as you don't have enough information to make that judgement.
 
Last edited by a moderator:
Again, the definition of extraneous needs to be googled.

I know what an extraneous conductive part is and what defines it (Extraneous-conductive-part: A conductive part liable to introduce a potential, generally earth potential, and not forming part of the electrical installation). How do you know it is not from the limited information the OP has provided regarding the copper installation pipework?
 
NO the incoming pipe is plastic.

Yes the incoming pipe is plastic, but the installation it feeds is copper. There is no information as to how extensive the copper installation is or whether it is all surface pipework on plastic clips or mostly buried in the concrete floor structure or it could even go back underground as copper to feed another building.

Without further information there is no way to know whether or not the installation pipework will be an extraneous conductive part.
 
Yes the incoming pipe is plastic, but the installation it feeds is copper. There is no information as to how extensive the copper installation is or whether it is all surface pipework on plastic clips or mostly buried in the concrete floor structure or it could even go back underground as copper to feed another building.

Without further information there is no way to know whether or not the installation pipework will be an extraneous conductive part.

544.1.2 says "The main protective bonding connection to any gas, water or other service shall be made as near as practicable to the point of entry of that service into the premises."

Since it refers to the point of entry of the service, rather than the point of entry of the pipework, it appears to be saying that, even if the reason that the copper pipework is extraneous is that it feeds out underground in copper, the main bond should still be made at the incoming point.
 
Yes the incoming pipe is plastic, but the installation it feeds is copper. There is no information as to how extensive the copper installation is or whether it is all surface pipework on plastic clips or mostly buried in the concrete floor structure or it could even go back underground as copper to feed another building.

Without further information there is no way to know whether or not the installation pipework will be an extraneous conductive part.

So the incoming pipe is plastic with a bond on it that's not needed. Ok we got there.
Yes it could go underground again (like the gas has and we said move the bond over to that pipe), and if it was copper then it would be bonded at that point would it not.
Am I right in thinking if a house had plastic gas & water incoming pipes and copper installation pipes that did not go underground again, you would bond the pipe work?
TJ, I think your comment of the word "Stupid" over steps the mark!!
 
544.1.2 says "The main protective bonding connection to any gas, water or other service shall be made as near as practicable to the point of entry of that service into the premises."

Since it refers to the point of entry of the service, rather than the point of entry of the pipework, it appears to be saying that, even if the reason that the copper pipework is extraneous is that it feeds out underground in copper, the main bond should still be made at the incoming point.

Which supports my point exactly.

Although you would have to check exactly what they mean when they say 'service' and how you apply it. I would say in the situation that it is not the incoming service which is being bonded but the installation pipework and as such would be best to be bonded at the point that the extraneous part enters the installation.
 
?
Yes. your interpretation is correct.
My immediate thought was that it should be bonded, but I couldn't understand why it hadn't been done as the gas supply is an easy connection within 2 metres of the CU and all services were put in at the same time, 10 years ago. The water stopcock and bonding point are miles away.
Pete


Did it comply then?
 
Which supports my point exactly.

Although you would have to check exactly what they mean when they say 'service' and how you apply it. I would say in the situation that it is not the incoming service which is being bonded but the installation pipework and as such would be best to be bonded at the point that the extraneous part enters the installation.

I agree. It would be better to bond at the point where the metallic pipework enters the building, which isn't what the regs appear to be saying.
 
544.1.2 says "The main protective bonding connection to any gas, water or other service shall be made as near as practicable to the point of entry of that service into the premises."

Since it refers to the point of entry of the service, rather than the point of entry of the pipework, it appears to be saying that, even if the reason that the copper pipework is extraneous is that it feeds out underground in copper, the main bond should still be made at the incoming point.
wrong.

then a block of flats only has bonding on the intake into the building and nothing in the flats?

each seperate building requires bonding in this case the house and outbuilding both need bonding
 
wrong.

then a block of flats only has bonding on the intake into the building and nothing in the flats?

each seperate building requires bonding in this case the house and outbuilding both need bonding

You misunderstand my point.

The regs seem to be saying that extraneous pipework have to be bonded where the supply (water/gas) enters, rather than at the point that makes the pipework extraneous, which could be where another building or an outside tap is supplied.
 
You misunderstand my point.

The regs seem to be saying that extraneous pipework have to be bonded where the supply (water/gas) enters, rather than at the point that makes the pipework extraneous, which could be where another building or an outside tap is supplied.

You need to drop the supply part, it could be uni-strut with tray that enters the building from outside in contact with ground. Supply service is just an example.
 

Reply to Bonding Gas Supply in an Outbuilding in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I like your way of thinking.
Replies
6
Views
626
loz2754
L
Although the gas pipe may no longer require the bonding, it should really be terminated correctly or completely disconnected at the other end...
Replies
2
Views
452

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top