Piratepete

Hi Guys
Doing an EICR of a property.
The client has an outbuilding with gas and water supplies. It has it's own CU fed from the main CU in the house.
The water is bonded but the gas is not.
The water supply is underground from the house in plastic and then changes to copper which is bonded.

The gas supply comes from the house in an underground copper pipe linked to the gas pipes in the house. So, electrically, it would be subject to the bonding in the house.
But does this negate the need to bond it in the outbuilding?

Looking forward to wise words!

Cheers
Pete:confused:
 
Last edited by a moderator:
You need to drop the supply part, it could be uni-strut with tray that enters the building from outside in contact with ground. Supply service is just an example.

I agree that main bonding may be required to extraneous parts other than services. However, where it is a service, 544.1.2 defines where the bonding connection should be made, namely where the service enters the premises.
 
I agree that main bonding may be required to extraneous parts other than services. However, where it is a service, 544.1.2 defines where the bonding connection should be made, namely where the service enters the premises.

Neither the gas nor the water in the outbuilding in the OP is entering the premises though, yet one certainly needs bonding and the other might.
 
I take it no one bothered to google the definition then?
BS7671 requires us to bond any conductive part which enters the building from outside, which may introduce a difference in potential.
There is no requirement to bond conductive parts that do not enter the building from outside.
The plastic water pipe is not conductive, so does not require bonding.
The internal copper water pipes are conductive, but as they do not enter the building from outside, they cannot introduce a difference in potential, and therefore also do not require bonding.
 
I take it no one bothered to google the definition then?
BS7671 requires us to bond any conductive part which enters the building from outside, which may introduce a difference in potential.
There is no requirement to bond conductive parts that do not enter the building from outside.
The plastic water pipe is not conductive, so does not require bonding.
The internal copper water pipes are conductive, but as they do not enter the building from outside, they cannot introduce a difference in potential, and therefore also do not require bonding.

I quoted the definition in previous post. What difference does it make if it becomes extraneous within the building or outside. If conductive pipework was buried in the floor of the house it could become extraneous.
 
Last edited:
I quoted the definition in previous post. What difference does it make if it becomes extraneous within the building or outside. If conductive pipework was buried in the floor of the house it could become extraneous.
You quoted the definition of an extraneous-conductive part, not the definition of extraneous.
It doesn't make any difference, as it's physically impossible for something that is entirely inside a building to also be extraneous.
If the copper pipework were buried in the ground, then the part that is in the ground (no longer inside the building) would be extraneous, and where the copper pipework re-entered the building would require bonding.
However as far as I'm aware, the copper pipework does not exit then re-enter the building.
 
Twenty three HOURS and fifty four posts later and you're all still arguing about this bloody copper pipe!!

How long would it have taken to find out by testing the damned thing with a meter & long bit of wire???

and it's you lot who think plumbers are a bit mentally challenged!! :laugh:
 
Staying with the OP's outbuilding installation, if the metal water pipework that's fed/connected to a incoming plastic pipe, enters the slab internally, say to supply something on the other side of the room it would be prudent to test for being extraneous. Which is going to be pretty certain that it will be, especially if it's been tied to the slabs rebar grid, and therefore will require main bonding. If however it's just been visibly clipped internally to the walls, it's unlikely that it will be extraneous and main bonding will not be required.

The incoming gas pipe goes without saying, will be an extraneous conductive part that will require main bonding...

And that just about clears everything up as far as these two services are concerned with this OP's outbuilding query!!!
 
The IET mandarins must be howling with laughter at the farce they’ve created!

Bring back the 15th.
Non of this is it, isn’t it, slap a bit of wire on it then it isn’t.

From the OED

Irrelevant or unrelated to the subject being dealt with: one is obliged to wade through many pages of extraneous material.
 
[ElectriciansForums.net] Bonding Gas Supply in an Outbuilding
Whoever did this was either confused or trying to make sure 'belt and braces' style. The incomer for the water before the stopcock is plastic. The floor it passes through is chipboard and the pipe drops down into a solem/void (timber building raised up on blocks). After the stopcock and meter it's all copper either clipped to joists or in stud walls.
 
View attachment 28056
Whoever did this was either confused or trying to make sure 'belt and braces' style. The incomer for the water before the stopcock is plastic. The floor it passes through is chipboard and the pipe drops down into a solem/void (timber building raised up on blocks). After the stopcock and meter it's all copper either clipped to joists or in stud walls.
nothing wrong with belt and braces, i wear them when its cold (attached to my sellopets)
 

Reply to Bonding Gas Supply in an Outbuilding in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I like your way of thinking.
Replies
6
Views
626
loz2754
L
Although the gas pipe may no longer require the bonding, it should really be terminated correctly or completely disconnected at the other end...
Replies
2
Views
452

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top