bonding house into 2 flats?
R
rapidrich
hi im currently working on a house being converted into 2 flats they will both hav there own db theres going to be 1 water suply in but they will hav seperate gas supply....i will bond to the indevidual gas pipes but do i run bonds from both db's to the 1 water in ?another thing is the gas in runs up the outside wall into the property under the floor boards to a cupboard suplying a boiler so do i bond wer it enters the building (under the floor boards ? or wer it visable in cupboard going to the boiler? thanx
so wat u are saying is bond outside the property ?
If you can't get an accessible bond within 600mm from the point of entry to the property,i would take it straight to the meter.That is the way i would do it mate.Mr NICEC said you can bond at the first accessible point from the floorboard.So tell me why i can't bond a gas supply straight behind the cooker if the CU is in the kitchen and the meter is at the other end of the house.No difference:D
From experience a house converted into flats it is a requirement to have separate water supply to each flat WRAS regs. As a new supply being plastic throughout including isolation valves is bonding necessary ??? - hope this helps
Yes it is if the plumbing in the flats is all copper.
if the gas meter is on the outside of the house then its got to be bonded 600mm from where it enters the property not where it becomes visable.
I havent checked in the 17th BRB, but there was a get out clause in the 16th regarding distance for bonding, and it was "or a close as practically possible" or words to that effect.
I should have checked as i had to bond a house recently on a CU swap cos it hadnt had any since it was built in 1970 odd. and the nearest i could get was about 8 feet from the meter on the gas without digging up the living room laminate flooring. I just put it as a departure, and i think 8 feet from the meter is a big improvement on the nothing they had before, and running a 10mm green and yellow cable around the outside wasnt going to happen either.
Cheers.........Howard;)
rapidrich,
SirKit Breaker,
TrueNAS JBOD Storage Server
