Bonding of conduit in kitchen floor | Page 6 | on ElectriciansForums

Discuss Bonding of conduit in kitchen floor in the UK Electrical Forum area at ElectriciansForums.net

Joined
Nov 23, 2013
Messages
233
Reaction score
62
Location
West Yorkshire
Bit of a debate today, advice please as regs book not possible to get in my hands until tomorrow. New job, apartments, in the kitchen there are 2 x 25mm conduits from an external wall to an island within the kitchen that is free standing, to be able to get the hob supply across and lighting with a spare in case any sockets are added at a later date. My question is, do these require bonding? Thanks in advance.
 
Got a belt off a tray with T&Es on it in a ceiling void a few years back. One length run across the void and was isolated from any earth. The cables dropped through the perforations with no protection and one must have been cut through because the tray was live which I discovered when I provided a path for it to the ceiling grid, never say never.
 
I asked a similar question of Elecsa a couple of years ago regarding T&E running through a backbox to identify a drop, before going through a wall. They told me that as long as the T&E is continuous, then the backbox does not need to be earthed, as the cable is insulated and sheathed.
 

Reply to Bonding of conduit in kitchen floor in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
When you say plus kettle, does this indicate you are needing 13A socket/s on the island and a hob supply? and then an oven supply on a tall...
Replies
5
Views
697

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top