Just finishing a domestic rewire, TN-C-S, RCD split board etc. The problem I have is that at the beginning of the works I ran 10mm bonding cable to the services, now all the building work etc is finished, I've gone to connect the water bonding near the incoming supply and the builders have replaced all (visible) copper pipes with plastic! How does this affect me in regards to bonding services? This is always a contentious issue with me anyway as I see builders replacing more and more copper with pvc making the bonding effectively useless, unless you pull the house apart running bonding cable everywhere.

Also, is there a minimum ohm reading I should be achieving for my bonding? It's a long run, 15m or so? Tried the regs book but can't find anything useful....aidiabatic equation maybe?

I am using this as my Napit assessment, and I'd like to have a definitive answer for him.

Thanks

paul
 
If the incoming water is plastic then no bonding required. That said if you've run the cable and you can attach it to copper you may as well do it!
 
hard one this ,cross bond near the boiler 10mm then bond as suggested at the stop cock then contiual bond across the plastic pipe work ( not cut ) and bond again on the copper pipe all metal work can become live under fault conditions (230vs) then test with low ohms across pipe work ,between socket screws to radiators ect you are looking for a max of 0.05 ohms this will show that all the metal work is bonded and will achieve a fault path of 50v and pop the breaker in the required time
 
I would think that the ideal solution is to put a short length of copper after the stopcock and bond to that.
I genuinely don't know the reason for not being allowed to bond before it is.
I'm sure someone will educate me fairly quickly :)
 
Can somebody help me here please?

Just finishing a domestic rewire, TN-C-S, RCD split board etc. The problem I have is that at the beginning of the works I ran 10mm bonding cable to the services, now all the building work etc is finished, I've gone to connect the water bonding near the incoming supply and the builders have replaced all (visible) copper pipes with plastic! How does this affect me in regards to bonding services? This is always a contentious issue with me anyway as I see builders replacing more and more copper with pvc making the bonding effectively useless, unless you pull the house apart running bonding cable everywhere.

Also, is there a minimum ohm reading I should be achieving for my bonding? It's a long run, 15m or so? Tried the regs book but can't find anything useful....aidiabatic equation maybe?

I am using this as my Napit assessment, and I'd like to have a definitive answer for him.

Thanks

paul


Refer to the regs.....the 17 Th!

Am I going to recite them no ! RCDs, max Zs, 1667 ?, disconnection times ? bonding requirements ? Do you actually know how to carry out a test for an Extraneous conductive part ? Do you know what it is ?
J
 
I've just recently read somewhere about the conductivity of water being poor and that the object of bonding is to bond the pipework that is extraneous.
I'm doing something rare here and sticking my neck out waiting for a potential barrage :)
 
Can somebody help me here please?

Just finishing a domestic rewire, TN-C-S, RCD split board etc. The problem I have is that at the beginning of the works I ran 10mm bonding cable to the services, now all the building work etc is finished, I've gone to connect the water bonding near the incoming supply and the builders have replaced all (visible) copper pipes with plastic! How does this affect me in regards to bonding services? This is always a contentious issue with me anyway as I see builders replacing more and more copper with pvc making the bonding effectively useless, unless you pull the house apart running bonding cable everywhere.

Also, is there a minimum ohm reading I should be achieving for my bonding? It's a long run, 15m or so? Tried the regs book but can't find anything useful....aidiabatic equation maybe?

I am using this as my Napit assessment, and I'd like to have a definitive answer for him.

Thanks

paul


You've got a Napit assessment and yet you are asking a question like the one I have highlighted???...............and you think the adiabatic equation applies to bonding????

They're going to seriously go down in my estimation if they pass you!


hard one this ,cross bond near the boiler 10mm then bond as suggested at the stop cock then contiual bond across the plastic pipe work ( not cut ) and bond again on the copper pipe all metal work can become live under fault conditions (230vs) then test with low ohms across pipe work ,between socket screws to radiators ect you are looking for a max of 0.05 ohms this will show that all the metal work is bonded and will achieve a fault path of 50v and pop the breaker in the required time


Is this a wind up - you must be having a laugh.

Cross bond near the boiler and then cross bond across every plastic insert.

What regs have you been reading.


What I don't get is how 'Jimmy Boy' can ask 'Paul' if he knows what an 'extraneous conductive part' is, yet proceeds to tick that he likes this post by you.......when you obviously don't know what an 'extraneous conductive part' is.

- - - Updated - - -

not part of the circuit but can become live under fault conditions or when the plumbers been lol


Wrong..........completely!!
 
You've got a Napit assessment and yet you are asking a question like the one I have highlighted???...............and you think the adiabatic equation applies to bonding????

They're going to seriously go down in my estimation if they pass you!





Is this a wind up - you must be having a laugh.

Cross bond near the boiler and then cross bond across every plastic insert.

What regs have you been reading.


What I don't get is how 'Jimmy Boy' can ask 'Paul' if he knows what an 'extraneous conductive part' is, yet proceeds to tick that he likes this post by you.......when you obviously don't know what an 'extraneous conductive part' is.

- - - Updated - - -




Wrong..........completely!!

wayne on the I Pad ticked wrong box genuine mistake dude
J
 
In this case the metal incoming service could introduce a different potential to that of the MET. Potentially increasing the touch voltage under fault conditions.
Hence recommending a short length of copper after the stop cock as regs state bond after it.
 

Reply to Bonding of services in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
296
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
840

Similar threads

The power company only brings in 3 wires which is 2 live and 1 neutral wire. It’s our responsibility to add the ground rod to bond the neutral...
Replies
3
Views
605
And if it's a garage then use metal clad accessories.
Replies
5
Views
412

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top