Right bit of a wake up call..
Definitions BS7671
Extraneous Conductive Part..
A conductive part liable to produce potential,generally Earth potential,and NOT forming part of the electrical installation .

Now how to test for this ? I know how to Biff over to you official forum troll LMFAO
J
 
This is a extraneous test...it's in GN8 ...
FFS learn !

DETERMINING IF A PART IS EXTRANEOUS OR JUST A PIECE OF METAL
A test should be made using an Insulation Resistance Tester set on MΩ, supplying 500 Volts.
Test procedure:
Connect one test lead to the metal part and the other lead to a known earth. (MET)


If the resistance value is 0.022MΩ (22000Ω) or greater, no supplementary bonding conductor is required.
If it is less than 0.022MΩ, supplementary bonding should be carried out.


From the Ohm’s law:


I = V / R;


I = 500V / 22000Ω = 0.023Amp


This shows that if the fault was on a single phase 230Volt supply the current that would flow between the conductive parts would of course be only 0.0115Amp (11.5 mA).


This current is unlikely to give a fatal shock.


Guidance Notes GN8 and GN5 state:
" If extraneous metalwork is above 22KΩ then it need not besupplementary bonded.
 
This is a extraneous test...it's in GN8 ...
FFS learn !

DETERMINING IF A PART IS EXTRANEOUS OR JUST A PIECE OF METAL
A test should be made using an Insulation Resistance Tester set on MΩ, supplying 500 Volts.
Test procedure:
Connect one test lead to the metal part and the other lead to a known earth. (MET)


If the resistance value is 0.022MΩ (22000Ω) or greater, no supplementary bonding conductor is required.
If it is less than 0.022MΩ, supplementary bonding should be carried out.


From the Ohm’s law:


I = V / R;


I = 500V / 22000Ω = 0.023Amp


This shows that if the fault was on a single phase 230Volt supply the current that would flow between the conductive parts would of course be only 0.0115Amp (11.5 mA).


This current is unlikely to give a fatal shock.


Guidance Notes GN8 and GN5 state:
" If extraneous metalwork is above 22KΩ then it need not besupplementary bonded.



Nearly right.
 
Dependi on the 'let go' ?
J

Yeh - and you forgot the bit about the resistance of the human body.

The equation is actually:

Rcp> (Uo/Ib) - Ztl


where,
Rcp is the resistance between the conductive part and the MET in ohms.

Uo is the nominal voltage to Earth in volts .

Ib is the value of current through the body in amperes that should not be exceeded.

Ztl is the impedance of the human body in ohms. The value suggested is 1000 ohms where Uo is 230 V (50 Hz), under dry or wet conditions.

Taking Ib as 10 mA and Ztl as 1000 ohms (as suggested above where the disconnection times in the installation are 0.4 s or less and Uo is 230 V), the limiting value of Rcp is given by:

Rcp > (230/0.01) - 1000

Rcp > 22,000 ohms


So, if RCP of metal part is > 22,000 ohms, then no main bonding required.


We all discussed it in some depth here:


http://www.electriciansforums.net/e...ns/16558-extraneous-yes-no.html#ixzz2Bg5wiQgp
 
I've just recently read somewhere about the conductivity of water being poor and that the object of bonding is to bond the pipework that is extraneous.
I'm doing something rare here and sticking my neck out waiting for a potential barrage :)
ultra pure water is a very poor conductor. it has been de-ionized to such an extent that it can be used as an insulator. you can get water with resistances upto 18 megohms. you have to store it carefully though, any contact with air will introduce ions back into the water. it is also a very strong solvent when kept in such a distilled state.
 
Your quite right Wayne I was of course just working on the recognised 10ma 'let go' figure based on a Ztl of 1000 ohms under dry conditions for a Uo of of 230v
J
 

Reply to Bonding of services in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

Similar threads

The power company only brings in 3 wires which is 2 live and 1 neutral wire. It’s our responsibility to add the ground rod to bond the neutral...
Replies
3
Views
605
And if it's a garage then use metal clad accessories.
Replies
5
Views
412

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top