I recommend you read Guidance Note 8 Earthing & Bonding
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Bonding of services in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I recommend you read Guidance Note 8 Earthing & Bonding
This is a extraneous test...it's in GN8 ...
FFS learn !
DETERMINING IF A PART IS EXTRANEOUS OR JUST A PIECE OF METAL
A test should be made using an Insulation Resistance Tester set on MΩ, supplying 500 Volts.
Test procedure:
Connect one test lead to the metal part and the other lead to a known earth. (MET)
If the resistance value is 0.022MΩ (22000Ω) or greater, no supplementary bonding conductor is required.
If it is less than 0.022MΩ, supplementary bonding should be carried out.
From the Ohm’s law:
I = V / R;
I = 500V / 22000Ω = 0.023Amp
This shows that if the fault was on a single phase 230Volt supply the current that would flow between the conductive parts would of course be only 0.0115Amp (11.5 mA).
This current is unlikely to give a fatal shock.
Guidance Notes GN8 and GN5 state:
" If extraneous metalwork is above 22KΩ then it need not besupplementary bonded.
Dependi on the 'let go' ?Nearly right.
Dependi on the 'let go' ?
J
ultra pure water is a very poor conductor. it has been de-ionized to such an extent that it can be used as an insulator. you can get water with resistances upto 18 megohms. you have to store it carefully though, any contact with air will introduce ions back into the water. it is also a very strong solvent when kept in such a distilled state.I've just recently read somewhere about the conductivity of water being poor and that the object of bonding is to bond the pipework that is extraneous.