he bloody well will, mate, if he's anywhere near competent. if you change a CU, then any dangerous parts of the installation must be rectified.

hence why I said about issuing a eicr!
then asked if they would want a clean one. Or just check MY work (fuse board and the EIC I issue it)
 
suppose you were a motor repair garage and a customer brought a car in for a new clutch. would you let him drive it away if the brakes were totally flicked?
 
suppose you were a motor repair garage and a customer brought a car in for a new clutch. would you let him drive it away if the brakes were totally flicked?

Customer asked you to change fuse board- she tells you she knows the fuse in spur for boiler is 13a on the ring 32a (c2- incorrect oc protective device!)
but she say dont you dare touch it!
i only want you to change my fuseboard give me a eic for it and then p** off!

are you going to change it or not?
 
Not sure why I said that they are already 25mm

just as a example really- when I change fbs for company I upgrade 16mm to 25mm (514.3)

let eat me guess you call the don do you? And you look like brad pit too? Bore off

So if the DNO fuse is 60A or 80A you would upgrade the tails? That is unnecessary work IMHO

As for 514.3 - so you are changing them because they are the wrong colour?
 
Evening guys

am looking into becoming registered with niceic so I can do on the side pjs and sign them off. (All above board)

was going to use my parents house as my niceic assessment.

change the fuse board, (will carry out a eicr before and after)
upgrade tails to 25mm main earth to 16mm and Gas is already bonded with 10mm at P.o.e
However incoming water is plastic- then has a metal valve then goes off again into floor in plastic again. (Currently no bonding)

1st question- where do I stand with water bonding?
Im guessing the best thing would be to bond at the 1st bit of copper after the plastic- but how can I determine where that is as it goes off under the floor (most of ground floor is tiles or lamanate floors)
-obviously need to get this correct for the niceic inspector.

2nd question:

am I correct in thinking as long as the new fuse board, tails/main earth/bonding (depending on aboves situation with water) are correct to bs7671 as amended, can there be c2 and c3 on the eicr issued as my work will only be the fuse board? As long as the c2 or c3 are clearly noted on the eicr.

and 3rd question:
the assessment is 1 larger job (fuse board) and one smaller job like a new radial circuit install. Correct?
can both jobs be at same address (in my case my parents house)

i know both of the mentioned jobs are notifiable works- and I have a electrician who is already niceic registered who will be willing to register them as a third party on my behalf.

look forward to reponse

cheers guys

joe
Chinese Burn, electric shock therapy, nails being pulled out, dental work, six of the best with the cane, the cat of 9 tails, all very painful, this OP, probably even more so.
 
Hi Joe,

The NICEIC don't currently allow their members to 3rd party certificate others work.

As part of the board change, you'll need to complete an EIC. This involves testing every circuit, so the inspector could ask you to retest that circuit in front of him. It would look poor if he asked you to test a circuit that has a defect on it.
 
Customer asked you to change fuse board- she tells you she knows the fuse in spur for boiler is 13a on the ring 32a (c2- incorrect oc protective device!)
but she say dont you dare touch it!
i only want you to change my fuseboard give me a eic for it and then p** off!

are you going to change it or not?

if the flex from FC U to boiler is 1.5mm and the fuse is there to protect the flex, then a 13A is OK. then manufactrurers instuctions insist on a 3A because they're too tight fisted to fit OCPD for the boiler. tin hat firmly in place.
 
One question I asked that questions my computancy was the water bonding. My gut instinct as a competent tester would be no it doesn't need bonding as the incoming is not a conductive material- but Sod's law if I didn't ask the question the niceic would be as misery as you.

Huh?

Any chance you could repeat that in an intelligible fashion?
 
you don't want a eicr. you need to complete a eic for the work you do. that will be for the CU change and as full set of test results for each circuit. therefore no codes. as for thew water. find some copper pipe that's accessible. IR test to MET. if you get > 22k ohms, then it's not extraneous and does not require bonding. it may well give a low ohms reading as it's likely to be bonded to the gas at the boiler.

Joe,

Tel's post which I've quoted above explains about testing to see if a pipe requires bonding. It either does or it doesn't!
 

Reply to Bonding to plastic water pipe in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I don't think anyone on here is going to say it needs replacing, some may even argue that it's not even a c3.
    • Like
Replies
3
Views
432
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top