Got a 2 gang 2way switch on downstairs hall, The switch for the upstairs circuit is fed from the downstairs circuit, lives cables( t& e) go in the wall and up across the finished landing floor and up to the upstairs 2way switch, live (just one) the goes up in wall to rose, borrow a neutral from upstairs circuit and hey presto, it works.

How do I fix this, without running new cables, as client just replastered, painted and layer new flooring.
 
Had the same problem a few days ago when changing c/unit. Had to put both cicuits on 1 mcb. Not ideal but it is clased as 1 circuit then. The only other way would be to disconnect the neutral to landing light and run a cable from down stairs lights to the landing light up the outside of building. Make sure you mark in c/unit that landing light is off downstais light and i would mark in back of landing switch that the switch has 2 circuits in it.
 
You have one of those curious old fashioned problems where a rewire wasn't a complete rewire but, most likely a CU change using old cables.
The least you can do without running either a separate feed or neutral to the upstairs landing light is to place both lighting circuits on the same RCD but separate breakers.
This is not a conventional circuit or compliant with BS761. Since you will not achieve isolation by one MCB alone.

I remember once being approached by a right 'Lone Ranger' painter and decorator, who said. "We rule the roost. If we didn't exist then the job would never get finished" It appears he maybe right.....
 
that is bad practice in my opinion, if this method is to be employed then both circuits must share same mcb for isolation purposes.

It depends what the loading is on each of the circuits and the diversity likely to be applied. Older properties seem to have less lights, newer properties are often loaded to the gills.
I'd agree its not compliant and generates ambiguity, but then, on the other hand the client doesn't want his paint work damaged so that leaves you with no choice but to condemn the circuit, and fight it out in the courts for payment.

If it was a consumer unit change then it would have been up to the sparks to check that the circuit's neutral wasn't shared before the work started.
 
Ackbar, you seem to be missing the point. With two lighting circuits each on their own mcb, and a shared neutral at some point on those circuits, if you isolate one mcb you can get backfeed from the unisolated circuit VIA the shared neutral. It is not about overloading a circuit, but ensuring electrical isolation when required.


Sent from my HTC Sensation using Tapatalk
 
No, I think I covered the points you have raised
1/ The loading, or lack of it, on each lighting circuit will determine whether or not to put them both on the same MCB
2/ As stated earlier, Isolation will not be achieved by one MCB alone.

It could still be achieved by mechanically linking them together so that there is a single point of isolation and the loading is catered for.

Doesn't it get complicated when:
A/ the sparky does check before doing any work
B/ An intransigent customer who would prefer to have nice paintwork and probably frilly curtains, rather than making sure all electrical systems were safe and compliant.
 

Reply to Borrowed neutral and how to fix in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
813
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

Often in old wiring, live to the downstairs switch, then in twin (or twin & earth) the two switched lives to the upstairs switch, and a single...
Replies
4
Views
347
  • Question
We just left it as it was, again the customer didn't seem too bothered, dont think she wanted me digging any further.
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top