Re: Borrowed Neutral discovered after changing CU
Ah but come on P&S, he left a note about "multiple means of isolation" :clown:
Ah but come on P&S, he left a note about "multiple means of isolation" :clown:
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Borrowed neutral discovered when changing CU and discussion on DIY CU change in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
What was the earthing arrangement?Ze was 0.4
Didn't check the resistance on the existing ring mains, but equally I didn't make any change to them - ergo I should not have adversely affected the safety of them by changing a fuse for an MCB.
I did test the RCDs, they operate as expected.
then left one neutral energised by two MCBs, nice for the next poor sod to get his hands spiked.
2/10 for effort
so you see overloading a mcb as a no no but your happy to overload a neutral cable?Oh go on, 4 at least ?
The neutral energised by two MCBs is VERY CLEARLY marked, surely if you see a note on a CU which states "WARNING: Multiple isolations required due to borrowed neutral in lounge" and states both the circuit numbers, and is directly below those MCBs, it would be noticed by anyone working on it.
I know it's less than ideal, but moving both lighting circuits onto one MCB would potentially risk exceeding the MCB rating, causing that to trip.
I was under the impression (having seen it before, albeit in a commercial building) that this was an acceptable practice.
If it's that big a cause for concern I could put them both onto the same MCB. I do actually value advice and constructive criticism given.
What was the earthing arrangement?
so you see overloading a mcb as a no no but your happy to overload a neutral cable?
Takes a few seconds to test continuity of ring and matters alot - why bother with Ze and rcd tests and not check you have a ring - makes no sense
Brilliant!!..... I'm done here, and so I'm guessing are mostOnly one room has a connection to that neutral, the rest of the downstairs lights have the 'right' neutral and no connection to the other (upstairs) circuit neutral, there is no risk of the neutral cable being overloaded by the addition of the lounge lighting - even with all the lights on upstairs.
Oh go on, 4 at least ?
The neutral energised by two MCBs is VERY CLEARLY marked, surely if you see a note on a CU which states "WARNING: Multiple isolations required due to borrowed neutral in lounge" and states both the circuit numbers, and is directly below those MCBs, it would be noticed by anyone working on it.
I know it's less than ideal, but moving both lighting circuits onto one MCB would potentially risk exceeding the MCB rating, causing that to trip.
I was under the impression (having seen it before, albeit in a commercial building) that this was an acceptable practice.
If it's that big a cause for concern I could put them both onto the same MCB. I do actually value advice and constructive criticism given.
eeek, fire fire ! hope the neutrals OK about it,
About the note, nice gesture but TBH, notes are not noted for being noteworthy, i wouldn't do it, especially in any commercial or industrial, its just not good enough.
So Rsmck, you have rewired your last two homes...
Did you carry out an adiabatic equation to ensure that your main earthing conductor and main equipotential bonding conductors were correctly sized?
Did you ascertain whether supplementary bonding was needed or could be omitted?
Were you able to differenciate between exposed and extranoius conductive parts?
Did you determine the prospective fault current prior to selecting over current protective devices?
Did you carry out the correct calculations to ascertain the current carrying capacity of each cable taking account of grouping, ambient temperature and thermal insulation?
How did you ensure that your voltage drop on each circuit was lower than the maximum allowed for the type of circuit?
Did you adhere to the building regulations with regards to the routing of each cable in structural walls and joists?
Did you ensure that cables buried in walls were routed in prescribed zones?
When performing your dead, then live tests, did you carry them out in the order specified in BS 7671?
How did you confirm continuity of main and supplementary bonding conductors, visually or by measurement?
What would have been the highest acceptable resistance reading for these?
Did you use test method one or two to confirm continiuity of circuit protective conductors?
What would have been the maximum Zs permitted on any of the ring final circuits on a B32 60898?
Did electrical equipment installed in special locations comply with its specific requirements?
How did you determine your maximum demand?
How were test results recorded, were they recorded on an electrical installation certificate as required by BS 7671?
Nope I just endanger us, no kids. I do have a partner, and she understands it about as well as me (maybe not much by your estimation) but we are both quite happy with the results.Do you have a missus and kids? Because if you do, please stop playing at something that you know nothing about! Replacing a socket and whacking up a new light fitting is one thing, but carrying out the sort of work you are talking about with a serious lack of the fundamental knowledge we as electricians are required to know is in my opinion idiotic! You endanger yourself and others!
Personally, no, but some people will - and some will do it safely.Would you replace your own boiler???