Borrowed Neutral on lighting circuit | on ElectriciansForums

Discuss Borrowed Neutral on lighting circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

R

Rikmac

Hi All
New to this forum.

Im currently doing a Electrical condition report on a domestic house that I have just fitted a dual RCD board and Equipotential bonding in

The Neutral on the landing light is taken from the downstairs circuit so is a C2 on the report
Its not practical to rewire this as the house is for sale and will cause lots of damage

My question is......
If I put both the upstairs & downstairs lighting circuit on one MCB will this comply?
I know two circuts one fuse is bad practice esp on a new board but is it a solution?

Rikmac
 
Hi All
New to this forum.

Im currently doing a Electrical condition report on a domestic house that I have just fitted a dual RCD board and Equipotential bonding in

The Neutral on the landing light is taken from the downstairs circuit so is a C2 on the report
Its not practical to rewire this as the house is for sale and will cause lots of damage

My question is......
If I put both the upstairs & downstairs lighting circuit on one MCB will this comply?
I know two circuts one fuse is bad practice esp on a new board but is it a solution?

Rikmac

If you take the definition of a circuit from the definitions section of BS7671, technically, the 2 circuits become one.
The disadvantage is that all lighting is lost should the applicable RCD trip.
 
Thanks for your reply
If I leave them on seperate MCB's they are still on the same RCD as both RCD's trip as soon as the light is energised so the solution is to put both circuits into one MCB to obtain a satisfactory result
Ill just put as a C3 that one MCB supplies both up & down lights?
 
Thanks for your reply
If I leave them on seperate MCB's they are still on the same RCD as both RCD's trip as soon as the light is energised so the solution is to put both circuits into one MCB to obtain a satisfactory result
Ill just put as a C3 that one MCB supplies both up & down lights?

No, if you put both 'circuits' into 1 MCB then there is no code to allocate.
You could make a note on the EICR to say why the circuits were combined and that the client declined remedial work.
 
Over the head transmission took place man... Could you be more detailed??? Thanks

Upstairs light on 1 circuit downstairs on another.......if split across 2 rcds both trip when light is turned on due to neutral been taken from upstairs circuit

This is a fail on a EIR as is C2 a defect

Put both circuits on the same MCB (circuit) then its ok

No defect just not good as if the RCD or MCB trip all the lighting will go off

In this case there is a pantry light so the fuse-board will stay lit

hope this clears it up for you
 
What the others said. However, always check for borrowed neutrals BEFORE changing a CU. That way, you can quote for sorting it out before committing to the job. Did you carry out any other pre-change checks or just hope for the best?
Are you doing an EIC or an EICR? They are very different.
 
as the house is being sold, it could be that the buyer's solicitors have asked for an EICR.
 
but if you change the board then an EICR wouldn't be the right certificate to give would it? it has to be a EIC surely unless things have changed overnight.
 

Reply to Borrowed Neutral on lighting circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
795
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
827

Similar threads

You too? I thought I was in a unique position:anguished::coldsweat:
    • Like
Replies
5
Views
265

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top