Have a look at 530.3.4 .
The way I understand
If the board is domestic and not exceeding 100 amp the board is covered by the suppliers fuse, the breaking capacity of the mcbs doesn't have to be greater than the PFC
Over 100 amps or non domestic the above wont apply
fuse size is irrelevent , the pfc is decided by how close the service is to the dno transformer - so even if your cut-out fuse is only 60A your pfc could be as high as 4Ka if youre 400 yrds from a local substation.
if you put 2ka fault through a 1ka mcb - it will operate but cease to work correctly from thence.
in essence , youre choosing a device that will be destroyed after tripping.
just read it twice , says absolutely nothing to suggest mcb ratings are anything other than whats stamped on them.
the reference to bs no is the standardised assemblies for CU's.