Hi all,
Was called to a job today with intermittent RCD tripping from the garage. Standard domestic TNS with three core SWA from the house to an (inaccessible) junction box down the side of the garage where it joins to 10mm T&E which then runs on surface plastic trunking to a metal-clad CU on an internal breeze wall (two rooms to the garage) about four metres away.
Previous chap has disconnected the circuit and told owners that the problem is probably damage to the buried SWA somewhere in the garden. I started by disconnecting the supply from the garage CU and doing an IR test from the house, and got perfect readings. However, once the supply was reconnected to the garage CU the LE reading was 0.59 MOhm (LN was still over 200 MOhm). This was the same even after taking out all of the downstream cables from the CU.
After a bit of head scratching I ended up taking the board off the breeze wall and found that, with the board dangling by the supply cable without being screwed to the wall, the readings were fine again.
The only thing I can think is that something funny is going on in the inaccessible junction box which is somehow giving the wall a potential. I didn't use a meter but the wall doesn't feel damp at all. Is that possible at all?
Any ideas gratefully received!
Thanks.
Was called to a job today with intermittent RCD tripping from the garage. Standard domestic TNS with three core SWA from the house to an (inaccessible) junction box down the side of the garage where it joins to 10mm T&E which then runs on surface plastic trunking to a metal-clad CU on an internal breeze wall (two rooms to the garage) about four metres away.
Previous chap has disconnected the circuit and told owners that the problem is probably damage to the buried SWA somewhere in the garden. I started by disconnecting the supply from the garage CU and doing an IR test from the house, and got perfect readings. However, once the supply was reconnected to the garage CU the LE reading was 0.59 MOhm (LN was still over 200 MOhm). This was the same even after taking out all of the downstream cables from the CU.
After a bit of head scratching I ended up taking the board off the breeze wall and found that, with the board dangling by the supply cable without being screwed to the wall, the readings were fine again.
The only thing I can think is that something funny is going on in the inaccessible junction box which is somehow giving the wall a potential. I didn't use a meter but the wall doesn't feel damp at all. Is that possible at all?
Any ideas gratefully received!
Thanks.