S

skamuk

My friends downstairs sockets are tripping the RCD. First thing I did is unplug everything on the circuit, switched on the MCB and the RCD tripped. Tested continuity of L-L N-N CPC-CPC between the legs. CPC has no continuity whatsoever. Could anyone advise me what would be my next step to determine where the break in the cpc is? Thanks
 
I take it only normal size house so safe way is to take off sockets one by one
Have done this. All connections are present and terminated ok. I now need to determine where the break is, bearing in mind all cpc are twisted together at each socket. Would I untwist all of them and test continuity between each socket?
 
Steps to take:

1. Get MFT out of van
2. Identify all sockets on circuit - draw plan
2. Set MFT to Zs
4. Go to each socket in turn and note value

If you are lucky you may see a "significant" drop in value at adjacent sockets - then take each off the wall and look more closely.
 
I had same problem disconnect cpc from
board rcd may stay up hence earth problem with neutral somewhere only takes a nip on the neutral to trip them things as far,as finding break in earth like previous said break the ring in middle and test one by one
 
Steps to take:

1. Get MFT out of van
2. Identify all sockets on circuit - draw plan
2. Set MFT to Zs
4. Go to each socket in turn and note value

If you are lucky you may see a "significant" drop in value at adjacent sockets - then take each off the wall and look more closely.

MFT wont do Zs, can do Ze and (r1+r2)/4... Seems like a long way round for me. I was planning to disconnect all cpcs on the circuit, untwist them all, then put wander lead on cpc leg 1 and test continuity at each socket, until I find the first socket in the ring, then do the same with the second cpc on leg 2 until I find the last socket in the ring. Once I've confirmed continuity between CU and first and last sockets I will move on to test cpc between each socket. Would this be the logical way to do it or a long way to do it?! - Also, would this not be the reason the RCD is tripping? Or will I need to locate a N-E / L-E fault somewhere as well? Thanks for your help everyone!
 
MFT wont do Zs, can do Ze and (r1+r2)/4... Seems like a long way round for me. I was planning to disconnect all cpcs on the circuit, untwist them all, then put wander lead on cpc leg 1 and test continuity at each socket, until I find the first socket in the ring, then do the same with the second cpc on leg 2 until I find the last socket in the ring. Once I've confirmed continuity between CU and first and last sockets I will move on to test cpc between each socket. Would this be the logical way to do it or a long way to do it?! - Also, would this not be the reason the RCD is tripping? Or will I need to locate a N-E / L-E fault somewhere as well? Thanks for your help everyone!


Really??
 

Reply to Broken CPC on ring final in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
277
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
269
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
298
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top