Without looking in regs have rcd spur units found their way back in book .I've been going through test sheets all day but I'll look after my spag boll.
531.3.4.1 bs7288 only provide additional protection.
 
Last edited:
There was mention on the forum at the time that they crept back in in the 1st amendment after being missed out in the initial 18th Ed.
It might have even been in a corrigendum (spelling!)
Yeh there def not in initial 18th but are in amm 2 with a note "only provides additional protection" and can be operated by ordinary persons
 
Yeh there def not in initial 18th but are in amm 2 with a note "only provides additional protection" and can be operated by ordinary persons
Well…. What else would you want them to be doing anyway?? By virtue of them being a socket outlet, fault protection is by ADS and over current protection by OCPD already.
 
These can also be FCU RCDs, which could be used to protect fixed wiring. For what ever reason, these can only be additional protection, and can't be used to meet disconnection times in the way that RCDs to BS61008 etc can be. (although the BS1362 fuse in it could be used to meet disconnection times).
 
These can also be FCU RCDs, which could be used to protect fixed wiring. For what ever reason, these can only be additional protection, and can't be used to meet disconnection times in the way that RCDs to BS61008 etc can be. (although the BS1362 fuse in it could be used to meet disconnection times).
Yes, but again an FCURCD won't protect the cables supplying it. It depends what exactly is meant by the statement in BS 7288.
 
Not sure I follow? You wouldn't normally install an RCD of any type and expect it to protect the supply cables, only those downstream.
No, you wouldn't. But my point is that it may be making it clear that those circuit conductors aren't protected, whereas with an RCCB or RCBO upstream they obviously are. Don't forget that not everyone thinks as logically as you do, so that may be where the statement has originated from. Just my opinion.
 

Reply to the thread, titled "BS 7288" which is posted in UK Electrical Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top