BS 7671 Regulation 532.6 AFDD | Page 2 | on ElectriciansForums
Discuss BS 7671 Regulation 532.6 AFDD in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hager are working on one the will work on a RFC rated at 32A, however Schneider can only offer one that will only work on a radial with a max rating of 25A. So in the future you will need to check the spec of what is installed when doing a periodic as there does not appear to be any standardisation across manufacturers as yet.
There's a surprise.
If you were considering installing AFDs in a domestic installation, you’d be looking at installing them on Shower or cooker circuits.
There may come a time where AFDs are required everywhere, but until that time, I’d limit their use.
There's a surprise. Not much thought given to this issue in my book, a knee jerk reaction by the IET.
I understand it’s a recommendation, but 532.6 says “shall be installed” which usually means “will be installed”
The helpline say, do a risk assessment when installing to explain why it hasn’t been fitted! I’ll just do that and as others have said, put it on the higher rated circuits for now and see what happens in amendment 1.
It says shall be installed because if you do elect to install one, then they shall be installed at the origin of the circuit.
It’s telling you were they are required to be
it’s a recommendation, recommend it to the customer along with the cost.......then write in the cert recommend and declined....
Reply to BS 7671 Regulation 532.6 AFDD in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
How many and what type of cables do you want to join, Chocbox is the last thing I would use.
I have just completed the 'Wallbox' on line courses. Seems to me that you need to install extra equipment (a Power meter) in the consumer unit to...