The relevant regulations are I think as follows:

BS 7671 513.1: cable joints must be accessible except where allowed by 526.3

which is covered by ...

BS 7671 526.3 (iv) joints made by welding, soldering, brazing or compression (which covers crimped connections)

So far so good. But:

526.5 (iii) Every termination and joint shall be in an enclosure partially formed or completed with non-combustible material.

This I think does not cover a choc box which is as far as I can make out is made of polyproplyne which is combustible.

Am I missing something?

I know you will all say I should use Wago connectors in a Wago box which is obviously correct, but I want to know how I should treat existing inaccessible crimped connections in a choc box in an inspection.
 
later ...

I found the specification for a Greenbrook CHOC30A which says it conforms To BS EN60670-22, which is the standard for "Boxes and enclosures for electrical accessories for household and similar fixed electrical installations". So these choc boxes comply with BS 7671 526.5 (i) "A suitable accessory complying with the appropriate standard", and are therefore actually OK.
 
How many and what type of cables do you want to join, Chocbox is the last thing I would use.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
reading

Thread Information

Title
Do crimped connections in a choc box in an inaccesssible location comply with regulations?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
peterinreading,
Last reply from
westward10,
Replies
3
Views
766

Advert

TrueNAS JBOD Storage Server

Back
Top