I have searched for an answer to this question but to no prevail.

BS3871's.... should these be changed? I have just done an EICR on a board with these and no RCD for lights serving bathroom but it has an RCD protecting all sockets, shower and the cooker circuit... now I have given 2 x C2 codes because 1 the RCD doesn't trip in the allowed time and 2 for no RCD protection or supplementary bonding etc for the lights in bathroom

BUT hypothetically... if it was all protected by a fully working RCD would I be ok in saying BS3871's are ok still? Or does it need to comply with regards to disconnection times? If so where do I find these disconnection times?

Thanks in advance
 
The location of the luminaire is not relevant it serves a location containing a bath or a shower, zones in this case are irrelevant.
IMO the location of the luminaire is relevant in some cases, from a coding point of view rather than compliance. If it could only be reached by climbing a ladder, then a C3 for no RCD and no supp bonding. If within reach, then C2 for the same
 
That would be 701.415.2, and 411.3.2.2, 701.411.3.3, 411.3.1.2, if this was a downlighter only accessible with a tool, how would you code that then?

I suppose in truth the sensible thing to do is to protect anything in a shower or bathroom with an RCD which in essence everything in a modern two RCD board is.
It is serving the location so whether a tool is required or not is neither here nor there.
 
True, but irrelevant. If no RCD was required when it was installed, then it's a C3.
You test to the current regs. Anything that doesn't meet the current regs, but met the regs. in force when it was installed is a C3*. Anything that doesn't meet the current regs, and didn't meet the regs in force when it was installed is a C2.

* I'm referring to 'modern' wiring, not stuff installed pre '50's, so please don't bring up fused neutrals.
Not really. A socket installed to an earlier edition which could reasonably be used to power equipment outside would be a C2 if no RCD protection.

I think you meant 'you inspect to the current regs' testing hasn't changed over the years (part for maybe AFDD's). ???
 
C2

Absence of supplementary bonding where
required, such as in a location containing a
bath or shower, where any of the following
three conditions are not satisfied:
❍ All final circuits of the location comply with
the requirements of Regulation 411.3.2 for
automatic disconnection, and
❍ All final circuits of the location have
additional protection by means of a 30 mA
RCD, and
❍ All extraneous-conductive-parts of the
location are effectively connected to the
protective equipotential bonding (main
earthing terminal).

So just because it was compliant 50 years ago doesn't mean it isn't a C2 on an 18th edition EICR
 
The latest best practise guide suggest that :
for class 2 fittings

Absence of supplementary bonding for installed Class II equipment where required (such as in a location containing a bath or shower), in case the equipment is replaced with Class I equipment in the future

this does not require reporting or any code
 
The latest best practise guide suggest that :
for class 2 fittings

Absence of supplementary bonding for installed Class II equipment where required (such as in a location containing a bath or shower), in case the equipment is replaced with Class I equipment in the future

this does not require reporting or any code
Who said the lights are class 2?
And what about the other exposed/extraneous conductive parts that may be simultaneously accessible?
If there is no RCD and no (or incomplete) supplementary bonding, then it's a C2.
 
I think what its saying is if all the equipment is class 2 there can be no exposed-conductive-parts , therefore the potential difference can not exist.
You cannot use Class II as a means of protection in an unsupervised installation such as a dwelling.
 

Reply to BS3871 on EICR classifiaction code? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
707
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
Surely one of the most important parts of supplementary bonding is to bond the radiator and hot tap/pipe to the cold one. Both the hot tap and...
Replies
32
Views
2K
  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
752

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top