Building control / works certificate | Page 3 | on ElectriciansForums

Discuss Building control / works certificate in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Main problem with the observations, is that they are badly worded.
Observation 1 for instance:
There is no requirement for there to be an earth between the metal front to the back box.
There is a requirement to earth exposed conductive-parts, which the back box could arguably be considered as such (if it’s metal).
As such the observation should be metal back boxes not earthed (or something similar).

Observation 4 is something that would be expected, because the cables would be longer. Not in itself an issue.

Observation 5 is not an issue.

Observation 11.
There are 3 voltage bands:
ELV (up to 50V), LV (50V to 1000V) and HV (above 1000V).
So to say that the voltage is not LV, means it is either ELV (good), or HV (very bad and also very unlikely).
The lack of earth may well be because the fitting is double insulated.

There’s quite a few there that are not issues, and some which are issues, but not necessarily related to the work conducted in 2005 and 2007.
 
By ******** - do you mean they're all minor issues, or actually not coded up the correct way, or in fact both?

A bit of both tbh..
Also in the test schedule the Zs values for sockets look dubious..

I find EICRs like this very frustrating, they are used as a legal document, a tool for knocking thousands off the price of houses, so come on let’s at least do a proper professional job of them
 
A very contentious report I must say

There is one obvious deficiency that can be agreed by all
There is a blank missing at the consumer unit o_O
 
A bit of both tbh..
Also in the test schedule the Zs values for sockets look dubious..

I find EICRs like this very frustrating, they are used as a legal document, a tool for knocking thousands off the price of houses, so come on let’s at least do a proper professional job of them
It's ok in our case we're not knocking £1000s off for this report.
 
Thanks for your replies. Much appreciated. It would - on a general level - be quite interesting to get 3 electricians to do an EICR on the same property and see what was / wasn't picked up. Not as a finger-pointing exercise but simply to see what different interpretations or focuses there may be.
 
Thanks for your replies. Much appreciated. It would - on a general level - be quite interesting to get 3 electricians to do an EICR on the same property and see what was / wasn't picked up. Not as a finger-pointing exercise but simply to see what different interpretations or focuses there may be.
Anyone want to do this in Sheffield in a couple of months time let me know :D
 
seems like there's a HV shower light? and missing blanK??? i'd have just put one in.
 
I wonder why he is still using 17th Edition EICR.
On a side note, to NAPIT, as a tutor I am forever trying to get students to use correct terminology and then I see "main earthing conductor" and "figure of 8 test" on this document.
 
I blame C&G courses which convince people they will become competent to carry out EICRs.

That's not the fault of C&G, more the companies that deliver the courses who falsely promise. There is actually a declaration for students to sign that they will not be electricians when they finish but improvers/mates
 
That's not the fault of C&G, more the companies that deliver the courses who falsely promise. There is actually a declaration for students to sign that they will not be electricians when they finish but improvers/mates
I am referring to the course for EICRs.
 

Reply to Building control / works certificate in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
501
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
974
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
907

Similar threads

Yeh im unsure without a photo of external box.
Replies
4
Views
261
Hello freddo (and everyone else who commented!), Thanks for your comment. Using that info, I now have this on the main: and this on the...
Replies
4
Views
307

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top