matt.smallbone
Des, I can now see the error of my ways, that's actually very true as the IEE has no regulation at all on the amount of cables in a breaker, only the suitability of the protective device for the cables. I take it back and apologise for my naff advice!!
Ill bare that in mind for future posts!!!
So actually there doesn't seem to be anything wrong with the cables in the breaker as long as they are adequately protected for the smallest CSA cable.
Ill bare that in mind for future posts!!!
So actually there doesn't seem to be anything wrong with the cables in the breaker as long as they are adequately protected for the smallest CSA cable.