Des, I can now see the error of my ways, that's actually very true as the IEE has no regulation at all on the amount of cables in a breaker, only the suitability of the protective device for the cables. I take it back and apologise for my naff advice!!
Ill bare that in mind for future posts!!!
So actually there doesn't seem to be anything wrong with the cables in the breaker as long as they are adequately protected for the smallest CSA cable.
 
Judging by your comment your no help at all, by judging from my comment you can decide on how competent I am, I don't think so mate, just trying to clear up an area that I hadn't come across before when issuing a eicr, wanted to get it right, I'm not looking to install a new DB just to get some extra money out of the job, just making sure I issue them with the right info and thank to all who have put in some helpful comments
 
Judging by your comment your no help at all, by judging from my comment you can decide on how competent I am, I don't think so mate, just trying to clear up an area that I hadn't come across before when issuing a eicr, wanted to get it right, I'm not looking to install a new DB just to get some extra money out of the job, just making sure I issue them with the right info and thank to all who have put in some helpful comments

I tend to agree with Mr Skelton on this one. These are questions I'd expect from an apprentice, not someone who should be fully qualified and, more importantly, very experienced in installation work to have moved on to doing EICRs.

And please don't spit your dummy out, this is a forum, and in the true spirit of a forum, this is just my opinion! :)
 
I wasn't trying to be helpful I was merely stating a fact. If you are contemplating a C2 for more than two cables in an OCPD then IMHO you are not competent enough to be carrying out EICRs. It may sound harsh but the notion that any old Joe (not saying that you are one) can carry out an EICR is deluded. Inspection and testing requires a lot of experience and an in depth knowledge of the subject and like I said, judging purely by your OP, these are skills you don't have. I may be wrong, hell we've all been guilty of asking stupid questions (myself included), but this is not something that someone who is carrying out such a task should be asking.
 
As I wouldn't install it like this and know its not to be installed like this but questioned wether it would actually be causing any real danger and if I needed to do anything about it, this is why I have put the question out there on this forum, codings on eicr's are to a degree with certain things down to the discretion, common sense and knowledge/experience of the inspector, now if I haven't got the correct knowledge or experience on if this should be brought up on an eicr report then the best thing to do is get a second opinion
 
As I wouldn't install it like this and know its not to be installed like this

Why can't it be installed like this? In centrally supplied systems I have had five or six conductors in one OCPD. Depending on their csa I would advise use of an appropriately sized ferrule to ensure a sound connection but done correctly there is nothing wrong with it.


if I haven't got the correct knowledge or experience on if this should be brought up on an eicr report then the best thing to do is get a second opinion

If you haven't got the correct knowledge or experience you shouldn't be carrying out EICRs. There is never anything wrong with second opinions, but asking others to do your job for you is another thing.
 
That's true actually, if it was an accessible joint I wouldn't have the same concern! And as far as I was aware it was a guideline set by the NICEIC that anything over two cable on a lighting MCB is deemed to be poor practise and if possible the circuits should be split on to separate MCB's.
And with regards to the spur from a ring in a consumer unit, that is a predicted method of connection again where possible as the joint or connection can be seen at the consumer unit and your not hinting for the connection, not always practical I know!!

The IET write the regulations not the NICEIC as they try to make everyone think.
 
As I wouldn't install it like this and know its not to be installed like this

Why can't it be installed like this? In centrally supplied systems I have had five or six conductors in one OCPD. Depending on their csa I would advise use of an appropriately sized ferrule to ensure a sound connection but done correctly there is nothing wrong with it.


if I haven't got the correct knowledge or experience on if this should be brought up on an eicr report then the best thing to do is get a second opinion

If you haven't got the correct knowledge or experience you shouldn't be carrying out EICRs. There is never anything wrong with second opinions, but asking others to do your job for you is another thing.

I'm not asking anyone to do my job for me there has been a mixed view on wether it deserves a code or not on this forum and from colleagues, friends, Everyone is going to come across new scenarios throughout there career that they may not have faced on an eicr meaning you will not have the knowledge or the experience
 
I'm not asking anyone to do my job for me

Yes you were, you asked "Does each lighting circuit need to be on its own separate mcb?"

Asking a second opinion however would have gone something like this; "I've come across an MCB with three seperate cables in it on an EICR, I haven't coded it because I cannot see any danger present but was wondering what your thoughts were"

there has been a mixed view on wether it deserves a code or not on this forum and from colleagues, friends

Which just goes to show how many misinformed 'electricians' there are out there.
 
I'm not asking anyone to do my job for me

Yes you were, you asked "Does each lighting circuit need to be on its own separate mcb?"

Asking a second opinion however would have gone something like this; "I've come across an MCB with three seperate cables in it on an EICR, I haven't coded it because I cannot see any danger present but was wondering what your thoughts were"

there has been a mixed view on wether it deserves a code or not on this forum and from colleagues, friends

Which just goes to show how many misinformed 'electricians' there are out there.

No I defo wasn't asking anyone to do the job for me, research is part of doing your own job, and this is a bit of Internet research, now your entitled to your opinion, wether someone takes it on board or not is another thing. So thanks for the input and good night!
 
Like kingeri said, there's no need to spit your dummy out, I'm just stating the obvious. Until I see evidence that you have the necessary experience to conduct the type of work you're doing I will naturally judge you by the first post of yours I see.

Again, if this is shown to me I'll be more than happy to eat humble pie but the facts so far are that you are asking the sort of really basic question you'd normally expect from a Electrical Trainee.
 

Reply to Bunched cables lighting circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
752

Similar threads

  • Question
Or a combined fitting in each row.
Replies
19
Views
2K
nicebutdim
N
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
768

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top