As I said earlier, these are in the remit if the inspection.It is out of the remit of testing but is it out of the remit of inspection?
Does the fitting comply with
416.2
Section 421
621.2(ii)
512.2
559.5.1
526.1
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Burnt out ballast EICR Coding in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
As I said earlier, these are in the remit if the inspection.It is out of the remit of testing but is it out of the remit of inspection?
Does the fitting comply with
416.2
Section 421
621.2(ii)
512.2
559.5.1
526.1
So you code things are not under the remit of BS7671?How anyone can no code a potential fire hazard caused by a light fitting is beyond me.
So you code things are not under the remit of BS7671?
Regulation 642.2 (iii)
The inspection shall be made to verify that the installed Electrical equipment is:
Not visibly damaged or defective so as to impair safety.
This is from the 18th edition so naturally it’s predecessor may be different but I do not have the 17th available at the moment to compare.
Now admittedly this forms part of the initial verification process but I’d be prepared to use the same regulation method for periodic inspection
Also see 651.2 regarding periodic inspection and testing note (ii) in particular
It’s almost the same(tongue in cheek) as a burnt out pin on a socket but ignoring it on the grounds that it’s not fixed wiring.I was going to look for a specific Reg tomorrow but I had absolutely no doubt that a Reg would be there to cover this.
How can anyone even think it is ok to no code this is beyond me.
It’s almost the same(tongue in cheek) as a burnt out pin on a socket but ignoring it on the grounds that it’s not fixed wiring.
Maybe lights should come under pat testing if we don’t inspect and code on an EICR
No I have already pointed put what remit they come under in the regs.Are you suggesting light fittings do not fall under BS7671?
It is worded differently in both book.Regulation 642.2 (iii)
The inspection shall be made to verify that the installed Electrical equipment is:
Not visibly damaged or defective so as to impair safety.
This is from the 18th edition so naturally it’s predecessor may be different but I do not have the 17th available at the moment to compare.
Now admittedly this forms part of the initial verification process but I’d be prepared to use the same regulation method for periodic inspection
Also see 651.2 regarding periodic inspection and testing note (ii) in particular
It is worded differently in both book.