On one of my sites, I have a 6 rising busbars ( E & I powerbar) rated at 250 A connecting a tap off box with a Schneider 100A isolator feeding a 3-phase board with 16mm SWA. I have around 24 tap off boxes onsite across 6 busbars and the installation is approximately 6 years old.
Over the past year I've had instances where the power has been completely lost. On shutdown and Inspection the busbar has burn marks and this has dropped out the phase; I've had to file the busbar and the tap off box connector to clear the residue in order to get this working.
This has happened to another box and the above works were carried out, but since we have had the voltage acting erratically and have been picking up 350V on two of the phases with just 50v on the third, which has burned out a significant amount of voltage sensitive equipment. The load on the board is well within the current carrying capacity and the SWA connections are secure on the tap off boxes. I've enclosed some pics to demonstrate. Has anyone else come across this or had experience of this.
Over the past year I've had instances where the power has been completely lost. On shutdown and Inspection the busbar has burn marks and this has dropped out the phase; I've had to file the busbar and the tap off box connector to clear the residue in order to get this working.
This has happened to another box and the above works were carried out, but since we have had the voltage acting erratically and have been picking up 350V on two of the phases with just 50v on the third, which has burned out a significant amount of voltage sensitive equipment. The load on the board is well within the current carrying capacity and the SWA connections are secure on the tap off boxes. I've enclosed some pics to demonstrate. Has anyone else come across this or had experience of this.