Hi, I need to extend a fire alarm, the panel is a CTEC CFP 2 zone one and currently it has a couple of apollo alarm sense sounder bases/heads on it. I fitted 2 extra normal (non-sounder) alarm sense bases and alarm sense heads but the panel is showing a fault on that zone, the fault clears if I bypass the two conventional base's. All the heads work on the sounder bases.
Are the alarm sense conventional bases compatible with the CFP panels because the instructions just show a diode base in the wiring diagrams, if they aren't then why do the alarm sense sounder bases/heads work ok.
Edit - I've just checked the CTEC site and it does say the panels are compatible with the alarm sense stuff. Why would it show a fault then if it clears when you bypass either base, they are definitely wired the correct way round. The bizzare thing is the panel still shows a fault if you put the end of line capacitor in the panel along with the fire alarm circuit if either base is in he circuit it that makes sense.
Edit 2 - I didn't get any instructions with the bases as they were just loose in the package but apparently you don't wire the alarm sense bases across L1 and L2, both browns go in L1. Fancy having an L2 connection then, its just inviting trouble, luckily they are only £3 each.
So you employed someone to install a fire alarm system but you are trying to sort the mess and the control panel, why?
The best way (not the cheapest )
Is to install a small single loop addressable pannel eg advanced or c tec xfp and 9 no sun rail zone monitors
This would be a compliant system
Did you badger the spark to install the system because he was cheaper than a fire alarm company? People ask me to do all the donkey work pulling in data cables and stuff for other people all the time, ok I'll graft my arse off pulling in all your cables and you turn up in a suit and tie, program it all and make 10 times as much as me, I don't think so.
This sounds like a typical installation that ends up with holes everywhere, chancers wired the fire alarm in a star configuration but probably daisy chained the network cables, don't you just love em.
Reminds me of a job we did last year, a 7 bed HMO, we priced for the electrics, emergency lights and fire alarm, we only got the electrics part as he had a mate "that could do fire alarms". I was there whilst he was installing it and I thought it was all a bit strange, he looped a piece of 4 core FP cable in and out of every point but it just ended up as a radial at the furthest away point ,no loop, no separate circuits, just one big radial. When it was finished he had just put a load of Aico smoke detectors at every point, no fire panel just domestic smokes. Not sure how that has gone down with the council/licencing body, I thought a HMO had to have a proper fire alarm system, I priced for an addressable system at about £5k. Also I still don't think he ever connected the emergency lights or the smoke detectors to the mains, he must have assumed I was going to do it for some odd reason.
If the wiring can't be corrected , the best solution is to get a cheap 1 loop addressable fire alarm panel and create a loop and install isolators at the fire alarm panel and connect each zone cable to a different isolator and change all the non addressable devices to addressable devices and then you can put each device in the correct zone and put in location text of each device
North West
United Kingdom
C-TEC fire alarm compatibility
oscar21,
Kenny212,
TrueNAS JBOD Storage Server