Good job Lenny.
Hope you don't mind but I added a few bits and pieces that I thought could be useful.
See what you think...
  • BS 7671 Cable Calculations.pdf
I like the clear layouts of both Lenny's and JUD's cable design templates
Just a couple of points
I would use U and Uo for the 3-phase and single phase voltages, respectively
JUD you have forgotten, in step 6, the Length of the final circuit being calculated.
Otherwise excellent stuff !
thts brilliant len, thanks
In step 6, do i have to multiply it by 0.001 to get ohms? i.e 4.91mohm/m x 9 metres x 1.2 x 0.001 = 0.053 ohms?
Or have i got it confused with something else, cheers mate
Yep or divide by 1000 (4.91 ÷ 1000) x 9 x 1.2 = 0.053Ω
It's all the same thing.
cheers mate
I enjoy doing cable calcs, so this is a perfect backup to make sure i'm always going in the right direction. cheers
Hi, I'm interested in seeing this spreadsheet as I'm doing cable calc's, trouble is all these books and tables are Blowing my mind. Can't seem to open it tho !! Any ideas ???
Reply to Cable Calc Template. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
    • Friendly
Well another week passed and I still don't have a proper answer to where the process is wrong. To reiterate, this is not a question for a real...