Cable Calc Template. | Page 2 | on ElectriciansForums
Discuss Cable Calc Template. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
so does that mean you would use the max zs reading of the breaker for the design???? sorry
No, the permitted device Zs doesn't come into the equation. The value used is the calculated theoretical of circuit Zs found by using the formula Zs = Ze+(R1+R2).
This theoretical Zs value is then used in a calc with the supply voltage to find the (I) component (which is the maximum earth fault current that could flow in a fault condition) of the adiabatic equation which is - S = sqroot of I squared x t divided by k.
The use of this equation with the correct information will then confirm wether or not the CPC of the proposed circuit is large enough to cope with the fault current that may flow in it.
I have been asked to connect a mobile home on a large transport site. The supply cable run is approx 250 meters. When I try to work out the voltage drop for the swa cable from size 25mm upwards there are three values in the regs book x,y,and z which shoul I use
Thanks anybody
Thanks anybody
Upto 35mm, I continue to use the resistive (r) component for calculating the VD. By moving to the impedance (z) component you will end up with a pessimistically large conductor size.
Going above 35mm and bringing reactance & impedance in to play makes it all a bit more complicated as power factors (if known) and temperature corrections come into play.
Have a read from page 312 (new green book) onwards (appendix 4).
Excellent, been meaning to knock one of these up for the back of my regs manual but aint had the time. A handy must to have a hard copy like this, especially the adibatic equation if you looking to save a few £££.. Why go large if theres no need!
Cheers
Reply to Cable Calc Template. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Well another week passed and I still don't have a proper answer to where the process is wrong. To reiterate, this is not a question for a real...