Hi,
Im doing some work on my 2400 Design and verification course (or whatever its called now) and i have drawn my circuits onto my building plan, but having worked out the outside lights they are way over for VD, i increased the cable size to 2.5mm from 1.5mm this helped, but not enough.
As i've already drawn it, separating into 2 separate circuits will make the drawing look ruff, so i was thinking of turning it into a ring circuit instead.
What do i need to change in my calc for the fact it is a ring?? i know that my cable length will increase but that alone makes it worse, what else do i need to do??
Circuit 8 - Outside Lights
Length of circuit - 65.5mts
There is 11 light fittings, each with 1x 150w lamp per fitting.
150w Ă· 230v = 0.65A per fitting
0.65A x 11 (fittings) = 7.15A (Ib)
After 90% Diversity is applied...
7.15A Ă· 100 = 0.0715
0.0715 x 90 = 6.435A (Ib)
(In) needs to be equal to or greater than (Ib), so (In) = 10A
Using table 4D4A from BS7671...
1.5mm Armoured cable using reference method D6 has a capacity of 22A
Volt Drop,
This is (mV/A/m) x Ib x Length of circuit Ă· 1000, so from table 4D4B...
1.5mm = 29 (mV/A/M)
29 x 6.435 x 65.5 Ă· 1000 = 12.22V
As this is a lighting circuit, it must be under 3% or 6.9V to be satisfactory. This fails.
Any thoughts???
Im doing some work on my 2400 Design and verification course (or whatever its called now) and i have drawn my circuits onto my building plan, but having worked out the outside lights they are way over for VD, i increased the cable size to 2.5mm from 1.5mm this helped, but not enough.
As i've already drawn it, separating into 2 separate circuits will make the drawing look ruff, so i was thinking of turning it into a ring circuit instead.
What do i need to change in my calc for the fact it is a ring?? i know that my cable length will increase but that alone makes it worse, what else do i need to do??
Circuit 8 - Outside Lights
Length of circuit - 65.5mts
There is 11 light fittings, each with 1x 150w lamp per fitting.
150w Ă· 230v = 0.65A per fitting
0.65A x 11 (fittings) = 7.15A (Ib)
After 90% Diversity is applied...
7.15A Ă· 100 = 0.0715
0.0715 x 90 = 6.435A (Ib)
(In) needs to be equal to or greater than (Ib), so (In) = 10A
Using table 4D4A from BS7671...
1.5mm Armoured cable using reference method D6 has a capacity of 22A
Volt Drop,
This is (mV/A/m) x Ib x Length of circuit Ă· 1000, so from table 4D4B...
1.5mm = 29 (mV/A/M)
29 x 6.435 x 65.5 Ă· 1000 = 12.22V
As this is a lighting circuit, it must be under 3% or 6.9V to be satisfactory. This fails.
Any thoughts???