S

Sparky83

Hi,

Im doing some work on my 2400 Design and verification course (or whatever its called now) and i have drawn my circuits onto my building plan, but having worked out the outside lights they are way over for VD, i increased the cable size to 2.5mm from 1.5mm this helped, but not enough.

As i've already drawn it, separating into 2 separate circuits will make the drawing look ruff, so i was thinking of turning it into a ring circuit instead.

What do i need to change in my calc for the fact it is a ring?? i know that my cable length will increase but that alone makes it worse, what else do i need to do??

Circuit 8 - Outside Lights
Length of circuit - 65.5mts
There is 11 light fittings, each with 1x 150w lamp per fitting.
150w Ă· 230v = 0.65A per fitting
0.65A x 11 (fittings) = 7.15A (Ib)
After 90% Diversity is applied...
7.15A Ă· 100 = 0.0715
0.0715 x 90 = 6.435A (Ib)
(In) needs to be equal to or greater than (Ib), so (In) = 10A
Using table 4D4A from BS7671...
1.5mm Armoured cable using reference method D6 has a capacity of 22A
Volt Drop,
This is (mV/A/m) x Ib x Length of circuit Ă· 1000, so from table 4D4B...
1.5mm = 29 (mV/A/M)
29 x 6.435 x 65.5 Ă· 1000 = 12.22V
As this is a lighting circuit, it must be under 3% or 6.9V to be satisfactory. This fails.


Any thoughts???
 
I have another question....

Although this is a colleague of mine who is also doing this course. He wants to use trunking, he has a lighting circuit that he can put on a 6A MCB, but when doing the correction factors calculation, the only one that has any relevance to him is the grouping factor.

So he would do In / Cg

Looking in the regs, his Cg is 0.03 as he has 30 circuits in this trunking.

6 / 0.03 = 200A
10 / 0.03 =333A

Is this correct?

Is his only option to use a separate run of trunking and split up the circuits?

Grouping factors in the regs only go up to 20 circuits. But extrapolating to a horrendous 30 circuits would only give you a grouping factor of about 0.3 not 0.03 which would require you to use a cable having CCC of 20A so you would be looking at 2.5mm2 and some large trunking.

It's also worth keeping in mind that circuits carrying less than 30% of their grouped current-carrying-capacity can be ignored when calculating the rating factor for the rest of the group. (Note 9 under table 6C in the red OSG)
 

Reply to Cable calcs? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
754

Similar threads

  • Question
As you have actually measured the cold resistance (R1 + Rn = 0.15) then you have the voltage drop at the expected current (60A) so you can compute...
Replies
2
Views
1K
  • Question
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
2
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top