C

Chris Electron

Hello,

Can anyone tell me please if you can use the figures given in BS7671 cable current carrying capacity when using 12V?

eg- so 1.5 multicore clipped direct can take 19.5A. Is this what the cable can carry for both 12V and 230V- or any other voltage?


Any help greatly appreciated!

Thanks,

Chris.
 
Thank you for all the messages. Am new doing a 12v installation within a domestic house 230v. Apart from sticking up recessed down lights. Have done all volt drop calcs etc. When Zs has been mentioned above it reminded me that I will need a circuit breaker. So you get 12v fuses? I guess they must be out there.
 
B&Q for your 12v fuses
Thank you for all the messages. Am new doing a 12v installation within a domestic house 230v. Apart from sticking up recessed down lights. Have done all volt drop calcs etc. When Zs has been mentioned above it reminded me that I will need a circuit breaker. So you get 12v fuses? I guess they must be out there.
 
So you get 12v fuses? I guess they must be out there.
The primary function of a fuse is to limit the current that can flow in the circuit so you select an appropriate fuse according to its rating in Amps.

As long as the voltage rating on the fuse is higher that your circuit voltage it's fine. You can use a fuse with a 500v rating on a 12volt circuit.
 
This 12v install is oddly off a leisure battery! It is all a bit odd. I have backed off from any 'design' now on this 12v circuit as it is all a bit DIY for my liking.
Any info on anything that I might need to add if using a leisure battery in this install?!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Cable Capacity
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
19
Unsolved
--

Advert

Thread statistics

Created
Chris Electron,
Last reply from
Chris Electron,
Replies
19
Views
1,832

Advert

Back
Top