No tin hat, plasterboard is rated at 30 minutes. After 30 minutes of fire would collapse be classed as premature?
Do you think 30 mins is a realistic time frame for the alarm to be raised. The Fire Brigade get to the property, set up, enter the building and put the fire out?
No tin hat, plasterboard is rated at 30 minutes. After 30 minutes of fire would collapse be classed as premature?
Just done a surface fire alarm install, 90% normal clips but fire rated ones to ensure the cable cannot fall or create a hazard in such a situation..
The misconception is that all the fixings have to comply yet the install has to satisfy the point the run will not collapse and get tangled in the gear of the fire brigade so a fire rated clip in suitable positions will be adequate.
I didn't think they would enter once the ceiling had collapsed? By that stage of the fire I can't imagine there would be anyone left alive to rescue?
The regulation was brought in to protect fire fighters. In a large building they certainly would clear out room by room.
But in a 'large' building, it would have additional fire preventative measures and fire fighting equipment. Not what the OP has asked.
The regulation was brought in to protect fire fighters. In a large building they certainly would clear out room by room.
That would be covered under different Standards. BS7671 does not state the size or type of building. It just simply states that all cables must be secured against premature collapse.
BS5839 -1
26.2 (f)
States methods of support should be non-combustible then goes to note 10 which makes the case that this recommendation precludes the use of plastic clips, ties and trunking..
(I can somewhat see why this regulation is misleading)
Now the interpretation of this regulation is somewhat ambiguous IMHO as all clips/ties or trunking in effect are supporting the cable in some fashion it could be argued so doubling the clips used even if not required could be taken they too are supporting the cable too, but I take from this is a cable needs to be suitably mechanically supported with fire rated solutions, if you can show this then there is no reason a number of the fixing cannot be just standard plastic fixings, BS7671 expand on this regulation.
Note here that BS7671 521.10.202
Note3 This regulation precludes, for example , the use of non metallic cable clips or cable ties as a sole means of support.
Note4 Suitably spaced steel or copper clips, saddles or ties are examples that will meet the requirement of this regulation.
This is as I have installed my system and meets the requirements set out in the BS7671 and that of the BS5839 in which the BS7671 expands on.
@essex
I have the BS5839-1 2017 and the BS5839-6 2013 which to my knowledge are still the latest versions.
Given that the regulation concerning fire rated supports in both the BS5839-1 and the BS7671 18th edition are there for the exact same reason and the body which designed and constructed these particular regulations are the one and the same then I would conclude that the BS7671 18th edition been the most up to date is the one that is accurate and thus in this case would mean it expands on the older version of the regulation in the BS5839-1.
I do not get why you think the BS5839 trumps the BS7671 as it is subjective to regulation, dates of release, amendment etc, I agree there will be extra regulation applicable under BS5839 but disagree with a sweeping claim that BS5839 always overrules, up until the recent release of the BS5839-1 (2017)there were forthcoming amendments found in the more recent versions of BS7671 in areas that crossed over that eventually were implicated in the 2017 edition ...