I don't think it's such a silly question. Two or more cables side-by-side, touching, under capping would bring the grouping factors into play and reduce their current carrying capacity. So if you have two heavily loaded cables, I'd put them under separate capping.
My god no, please not an arms member as well, thats it, I'm going to get drunk, jeez
A pointless exercise trying to do this, if you are wiring a lighting circuit for example in a house using 1.5mm2 conductors and behind the capping is a twin and 3 core to the switch as standard 2 way switching, then why would we ever consider grouping? why? alternatively, if we cap from behind the skirting board up to 450mm2 from FFL to a socket outlet and there are 2x 2.5mm2 6242Ys why would we consider grouping? why? if there is a 2.5mm2 and a 1.5mm2 cable behind Capping I would have to ask why these 2 differently sized cables were together in the first place????
A pointless exercise trying to do this, if you are wiring a lighting circuit for example in a house using 1.5mm2 conductors and behind the capping is a twin and 3 core to the switch as standard 2 way switching, then why would we ever consider grouping? why? alternatively, if we cap from behind the skirting board up to 450mm2 from FFL to a socket outlet and there are 2x 2.5mm2 6242Ys why would we consider grouping? why? if there is a 2.5mm2 and a 1.5mm2 cable behind Capping I would have to ask why these 2 differently sized cables were together in the first place????
Since the OP hasn't said what these cable are for, you're just guessing.
?"
A bit of advice, give it up now before you cannot see the top of the hole your digging.