Hi ,how do you check the resistance of a cable thats about 140m long, goes through 3 consumer units and between the consumer units it is different sizes
 
How about answering the question
thought i did in post#2. measure the resistance of each section, the add them up. low ohm meter, then a pencil and paper ( or , if you are flush, a calculator.)
 
Use a low resistance ohmmeter and a zeroed (very) long lead to measure the resistance of each section and add the resistances together.


If you have more than one of the same size conductor connect the conductors together at one end and measure the resistance between the two conductors at the other end and halve the result to get the resistance of one conductor.
 
I am no spark,but at least I know it,just spent 10k on a solar PV system ,the so called trained electrician never checked the AC cable like what has been sugested and now it does not work and all he wants to do now is increase the paramiters of the inverter
 
I am no spark,but at least I know it,just spent 10k on a solar PV system ,the so called trained electrician never checked the AC cable like what has been sugested and now it does not work and all he wants to do now is increase the paramiters of the inverter
How about getting him to provide a test certificate for the job done. For the 10k paid, I think it should be expected.
 
Last edited:
How about answering the question

Exactly what you should be asking your electrician, not coming on to an electricians forum and demanding it from us. All of us here love to help when we can, if we think it is appropriate. In this case, you need to talk to your electrician, not get advice on how to put yourself in danger.
 

Reply to cable problems in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
To give you some idea....with my DNO, the question "Can you see arcing, sparking or smoking?" is 3.5 minutes into the automated call answering...
Replies
8
Views
611
  • Question
Can imagine getting a 6mm through an existing conduit of 22mm with a cable already in might have some challenges in it’s self. Obviously not been...
Replies
15
Views
3K
  • Question
Better off with the click prw213 as it has twin screw termination.
Replies
9
Views
757
Sounds more positive.
Replies
8
Views
472
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
637

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks