DurhamSparky
another mind blank..
2.5mm cable on radial rated at 16A in DB powers 4 sockets in loft area, i have tapped off this supply into 1.5mm cable to power 5x 50 watt downlights, would you install a FCU rated at 3A for the lights or would you be happy leave the 16A MCB as protection..!
the 1.5mm cable is clipped direct to joists and does not come into contact with any insulation so de rating factor has little impact!
2.5mm cable on radial rated at 16A in DB powers 4 sockets in loft area, i have tapped off this supply into 1.5mm cable to power 5x 50 watt downlights, would you install a FCU rated at 3A for the lights or would you be happy leave the 16A MCB as protection..!