What a pain! So if there are only three terminals in the block then I could get by by using one 6mm tail only but if there are three sets they have to be strapped out. Did you use 2.5 for the straps.
It was quite a while ago now, but I don't think 3X 6mm fit in the blocks, so I probably used 2.5mm for the straps, also for the earths straps (sleeved), these straps (links) were only about 40 or 50mm long or even less.
I know the instructions specifying 3X 2.5mm 'tails' adds up to 7.5mm, but you are using only 2.5mm per internal circuit and the supply cable fom the DB to the isolator and connection plate is only 6mm for the rest of the entire run.
Managed to get instruction manual from Beko. Only three terminals to worry about for connection - so no linking :-) Also copy attached of Tech Spec
Hi,
Have look at the fuse/mcb rating row on your Datasheet, it lists either 1X 32A or 3X 16A, as Des said some of these are to cater for threephase supplies.
As I said some have three connections, and some have the metal comb (internal links) already fitted.
The biggest problem trying to fit 3X 2.5mm cables is not where they terminate in the block, or blocks, but where the cable grip needs to hold the cable.
If you think about what I said earlier, in that the distribution circuit is almost certainly 6mm (on a 32A MCB), throughout it's entire length, why would you need 7.5mm for the last metre or so ?
I normally follow the Manufacturer's guidence, but in this case I think something has been lost in translation (Turkish> English), and think some common sense should be applied.
Edit: it would make sense to use 3X 2.5mm cables on 3X 16A MCB's for three phase, and a single 6mm for single phase using a 32A MCB.
Three phase configuration may not neccessarily be for UK use.
Edit II: The 2.5mm the sheet refers to could also be flex, rather than T+E.
Sorry, I'm confused. At the end of the day you want to end up with a 6mm feed to either a cooker control or a cooker control with integrated socket, and that's it. Nothing else. You don't want any additional cable going to a socket. It should be a radial circuit that terminates at the cooker switch. Or am I misunderstanding?
so how do you connect the cooker then? i normally go from the cooker switch into a cooker outlet plate, in this case i think the cooker outlet plate has been replaced with a socket, probably because the oven is a 13A oven which came with a plug on
Depends on the installation method.......4mm can carry 37amps if clipped direct or embedded directly in plaster. 4mm radials on 32a breakers are quite common, usually for socket circuits.
Your question seems to hinge on deciding what size cable you have, something which we can't answer remotely on a forum. Take a sample of it to the wholesaler or even to the big orange shed and compare it to 4mm and 6mm on sale there! Or post some to me and I'll tell you what it is! 4mm is a bit bigger than 2.5mm.....6mm is quite a bit bigger......as I said earlier sparks can usually tell the difference at a glance. You could measure one of the strands and calculate the csa that way, if you have the right equipment (a vernier caliper).
The easiest way to tell the differnce is by the size of the earth, 4mm T+E has 1.5 and 6mm T+E has 2.5.
The socket is going to be replaced with a cooker connection outlet. As I said earlier it was probably for a previous oven with a plug.
Thats a useful comment. I've got 6mm but not any 4mm. Never ever used it. For curiosity how many strands does it have?
- - - Updated - - -
3 x 2.5mm cable means a 3 core flex, with each core being 2.5mm. You have one conductor terminated in each of the 3 terminals. It does not mean 3 lengths of 3 core run in parallel.
The alternative mentioned earlier of 5 x 1.5 mm cable refers to a single length of 5 core flex, with 1.5mm conductors, for using with 3 phase supplies and appliances. Again, only one conductor in each terminal.
Cable size and live wire colour change
Fleetwood,
Doug,
TrueNAS JBOD Storage Server
