Part of the range cooker Biff but because of the way induction hobs work apparently on IET site they run at the rating they are given by the manufacturer. It's specified on the cooker that the hob takes 7.8kw.
 
Last edited by a moderator:
and what are the chances that all hob rings will be in use at once ? thats what diversity is for.
the rating of the hob itself is irrelevent - its 1 appliance with a total load of 14.9 kW , this is the figure we use for calculating mcb & cable size.
so its still 32A.
 
There are elements that can't be used while other elements are in use on the oven section, so all the manufactures are telling you is the connected load, not it's ''Actual'' FLC.

The diversity factor for cooking appliances up to 15 KW have been used for over 60 years because they work and have on-goingly proven to work. So as your stated load is 14.9 KW, it will apply to your cooker too...

I have an induction hob and a double oven at home, ....never seen the manufacturers KW rating ever!!!! All wired in 6mm singles on a 32A RCBO... How much more convincing do you need?? lol!!!
 
Here's a practical example.

Re-wiring a house was spec'd a oven which was a dual fuel range - gas hobs and electric oven(s) - I think the max power was about 7kW, so duly run in some 6mm. When the range turns up I notice the cable with it was a 10mm, looked further and saw the oven had a rating of something like 17kW, nothing like what was spec'd. Warned the project manager that potentially this cooker could trip the 32A RCBO and I couldn't replace the cable without a big upheaval! That was over 2 years ago, hasn't tripped yet (touch wood) and its a rental property now and had a couple of diffent families in there.

If it did trip I could put a 40A RCBO in as the cable is in fact BS8436 and the CCC is much greater than T&E!
 
I can vaguely remember a mate going to install a rangemaster (for a blue chip comp) and he ended up ringin the manufactures and was told to wire in 10mm, dunno if that helps.
 

Reply to Cable Size in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
192
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Thanks for the swift response.
Replies
2
Views
596
  • Question
Well another week passed and I still don't have a proper answer to where the process is wrong. To reiterate, this is not a question for a real...
Replies
2
Views
276

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top