back to page 123 of osg and read post 32 again to calc It

no point telling you the answer if you can't explain it ;)
 
cable size??

It =24/0.8 = 30

can you find the cable size from table 6D1 page 128 of OSG?
 
What a complete knob I am , sitting in bed watching Darren Brown doing calcs in me head, plonka plonka plonka
anybody else want throw in a few insults its open season for me

But only unit 6am tomorrow so get in quick
 
remember voltage is 400V so can expect to get considerably more power and 3x that because there are 3 phases :)

You would also see if Vd was ok using Vd = Ib x Length x mV/A/M (value found from table 6D2) it turn out ok - well less than 5%

These lecturers always keep the really tough questions til last means they won'tbe stuck withnothing to do at the end of the lesson ;)

hope i've been some help and not made some stupid mistake somewhere.
 
Think your all wrong here . 50kw is 217.39 amps split over 3 phases , 72.46amps per phase. its oven resistive load. nearest breaker 80amp triple pole . instaled in trunking ref meth 4 , 3or more cables . requires 35 mm cables. rating 89amps. from quick look . night all. Michelle.
 
so how would the lay out work? i take it its just ran out the CU

you have been a great help thank you very much
 
Think your all wrong here . 50kw is 217.39 amps split over 3 phases , 72.46amps per phase. its oven resistive load. nearest breaker 80amp triple pole . instaled in trunking ref meth 4 , 3or more cables . requires 35 mm cables. rating 89amps. from quick look . night all. Michelle.

I wouldn't bet my life on me :D but your 217A figure comes from using 230 volts! It is 3 phase so you should use 400V and root 3
 
so how would the lay out work? i take it its just ran out the CU

you have been a great help thank you very much


probs to an isolator then to the motor - remember there is an mcb for each phase and if it is a motor they won't be type Bs

you still not seeing that button lol
 
brain in gear (just)

50x1000 50000
1.73x400 692 = 72.25a ( no correction factors taken into account)
 
brain in gear (just)

50x1000 50000
1.73x400 692 = 72.25a ( no correction factors taken into account)

correct and then share between 3 phases.

Edit: on reflection think your 72A is Il (line current) as the formula is for total power! so factors and mcbs should be done on that figure oops!
 
Last edited by a moderator:
cheers mate


Hey - you found that button :D

Edit ; when you have time have a read of the OSG chapter 6 and Scadden is a brill book for the theory - believe there is a new edition out now as well - well worth buying to get you thru your exams.
 
Last edited by a moderator:
just logged on to the office pc and computer says---

50kw - 90.32 amps length 50m voltage drop 11.29a type d mcb didnt allow for correction factors


Good Night
 
Last edited by a moderator:
soo what you are saying is the total power is 72A this then needs to be shared with 3 phases witch brings it to 24A per phase?
 
calculate the desing current w/1.732 x 400 and that will supply current per phase (is what i should of said) unless there is a pf involved
 
Last edited by a moderator:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
cable sizes
Prefix
N/A
Forum
Talk Electrician Forum
Start date
Last reply date
Replies
81

Advert

Thread statistics

Created
james king,
Last reply from
james king,
Replies
81
Views
11,097

Advert

Back
Top