so 70mm is way to big then if each phase only needs to caryy 24amps????????
so 70mm is way to big then if each phase only needs to caryy 24amps????????
is it not 24.73amps
so how would the layout work then can u explain of where the come out from the DB ?
whats the run?
Im off to the van to get me book
huh 6mm that what i got from 30A 6mm??
Think your all wrong here . 50kw is 217.39 amps split over 3 phases , 72.46amps per phase. its oven resistive load. nearest breaker 80amp triple pole . instaled in trunking ref meth 4 , 3or more cables . requires 35 mm cables. rating 89amps. from quick look . night all. Michelle.
so how would the lay out work? i take it its just ran out the CU
you have been a great help thank you very much
brain in gear (just)
50x1000 50000
1.73x400 692 = 72.25a ( no correction factors taken into account)
wat type mcbs for motors?