Safe zones are only vertical or horizontal, you'd have to wire in earthed steel conduit or use an earthed sheathed cable to go point to point with low voltage (230v) lights. Or use extra LV lights from a transformer to go light to light not in a safe zone.
If you do lights like this it's worth thinking about how failed units would be replaced, often installs like this are done with no thought for how to access for repair when it goes wrong.
my method is easier, cheaper, and cables are accessible. you can actually get decorative trunking and make a feature of it.
I think you are thinking of Flexshield cable?the name escapes me now...ask your wholesaler.
Thanks mate, thats what I thought ??Hi - as far as I know - flexible conduit is not sufficient so that zones may be ignored.
I agree it would take some messing about to bend it at each box, the cable you quoted looks much easier but not cheap and only sold in 100m drums. I will see if i can source is in smaller quantities.Any conduit used must be earthed and suitable for use as a cpc, as above, no flexible conduit I've used is suitable for use as a cpc. I'm not really sure how you could easily adapt steel conduit to this, an earthed sheathed cable would be better, there is a cable designed just for this ,to be used just like a buried T/E, the name escapes me now...ask your wholesaler.
Edit....It's listed as Shielded LSOH on the CEF website, and meets the requirements for a buried cable outside of a safe zone
This is what i was thinking but couldn't find anything relating to a staircase or diagonal plane... I usually work on commercial/industrial so was hoping someone could point me towards a reg saying i could go point to point but it seems there isn't oneInteresting one, although regulations denote a vertical or horizontal plane I feel this is one given the skirting run could contend for a exception in future regulations, it is a obviously clear assumption to make a direct diagonal plane to wire such a set-up, why the regulations specify vertical and horizontal is to give recognisable zones on a open plan wall, this however could sit in it's own exception.
Yeah £87 for 100m and i probably only need 20mLooking at Regs (nothing on tel...) 522.6.202 says (in part) use zones or comply with 522.6.204 which says (in part) BS8436 cables are ok. Edwardes also have that cable in 1.5mm .
Ive just done a listed stately home in pyro, dont want to go near it again ?MICC - polished copper, anyone?