Ive just read the report , try this: http://www.google.co.uk/url?sa=t&rct=j&q=eca%2F%20era%20report%20on%20conductors&source=web&cd=1&ved=0CEsQFjAA&url=http%3A%2F%2Fwww.wiley.com%2Flegacy%2Fwileychi%2Feca_wiringregulations%2Fsupp%2FAppendix_16.pdf&ei=cqCuT9KFG4LU0QWzhai0CQ&usg=AFQjCNEm0O1r9ZSztXLNacYz8Fyv7PFnEQ
to summarize, the only cables that will not meet disconnection times using armour as CPC are: 120 and 400mm2 2 cores. These are rare cables to install anyway.
If by bad design, you find that your Zs values will not be met, then a CPC at least 1/4 of the pahse conductor can be used.
IMO, if your using very large cables, then they are either to feed DB;s or large machines.
If your feeding a DB in an envbiroment with little or no extraneous metal, then i would probably use an external full size CPC, in order to keep the size of my final circuits down in order to meet Zs values. In an environment where there is lots of extraneous metalwork, then i would probably be happy to use the armour as CPXC, providing the envromental conditions allowed.
If your feeding a large machine opr motor, then fruther manufacturers guidance would be used, and the use of an external CPC would probably be neccesary.
All of the large pumps i install, have external CPC's that are smaller than the phase conductors. But they also have lots of other SWA cables running in paralell. The distibution of fault currents cant be equal, or all of the cables would fry. On one job i fed a 160Kw motor with 150mm scpre, and it had a 25mm2 external CPC. the fuse size was 315A, and it was fed via a VSD.
to summarize, the only cables that will not meet disconnection times using armour as CPC are: 120 and 400mm2 2 cores. These are rare cables to install anyway.
If by bad design, you find that your Zs values will not be met, then a CPC at least 1/4 of the pahse conductor can be used.
IMO, if your using very large cables, then they are either to feed DB;s or large machines.
If your feeding a DB in an envbiroment with little or no extraneous metal, then i would probably use an external full size CPC, in order to keep the size of my final circuits down in order to meet Zs values. In an environment where there is lots of extraneous metalwork, then i would probably be happy to use the armour as CPXC, providing the envromental conditions allowed.
If your feeding a large machine opr motor, then fruther manufacturers guidance would be used, and the use of an external CPC would probably be neccesary.
All of the large pumps i install, have external CPC's that are smaller than the phase conductors. But they also have lots of other SWA cables running in paralell. The distibution of fault currents cant be equal, or all of the cables would fry. On one job i fed a 160Kw motor with 150mm scpre, and it had a 25mm2 external CPC. the fuse size was 315A, and it was fed via a VSD.