Hi..I should probably know this but don't do too much 3 Phase stuff!!

Can anyone give the formula for working out the size of a 3 phase MCB?

I have a 12kw 3 Phase fryer to install.

Cheers
 
[ElectriciansForums.net] Calculate 3 Phase MCB size
 
So further to this, I need to calculate the cable size for a 40amp 3 phase MCB. Do I just base it on the CSA per phase i.e 6mm?

In a way. There are differences. E.G. if you look at Table 4D4A you will see that for a cable clipped direct, the max current is 49A for single phase but 42A for 3 phase.
All other installation criteria's have got to be taken into account as well.
 
Where have you got 40A from.
40 amps to supply 4 way board.

Way 1 12 kw Fryer..3 phase 16 amp mcb (Thinking diversity will bring it below 16amps)
Way 2 6 kw Grill...3 phase 10 amp mcb
way 3 L1 16 amp socket circuit
L2 10amp for 2.2kw water heater
L3 Blank
Way 4 L1 Blank
L2 6 amp Lights
L3 16 amp socket circuit

I'm really struggling for power as the site is maxed out so can't go over the 40 amp 3 phase supply.

Hope the above looks ok...someone will tell me if not. Just at planning stage at mo.
 
total oad estimate including sockets is c.25kW. split ove 3 phases this equates to 8.3kW per phase, assuming loads are closely balanced. c. 36 A per phase, so 40A per phase should just cope.
 
I'd look at moving some loads off L3 onto L1 depending upon the load balancing at the supply.

Although the fryer and grill are high loads once up to temperature this will drop as they start cycling through heating and cooling.

What sort of lighting is installed? I doubt it would be 6 amps, I'm guessing a small commercial kitchen so probably a couple of floro tubes and other lighting so around 2 amps.

What loads are plugged into the socket outlets?

Is the eater heater instantaneous?
 
In a way. There are differences. E.G. if you look at Table 4D4A you will see that for a cable clipped direct, the max current is 49A for single phase but 42A for 3 phase.
All other installation criteria's have got to be taken into account as well.

I'd look at moving some loads off L3 onto L1 depending upon the load balancing at the supply.

Although the fryer and grill are high loads once up to temperature this will drop as they start cycling through heating and cooling.

What sort of lighting is installed? I doubt it would be 6 amps, I'm guessing a small commercial kitchen so probably a couple of floro tubes and other lighting so around 2 amps. Yes, just a couple of led strip lights, 8 led lamps and 2 emergency lights

What loads are plugged into the socket outlets? Just hand held kitchen appliances, fridge, freezer etc

Is the eater heater instantaneous? No, under sink 10l heater
 

Reply to Calculate 3 Phase MCB size in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
395
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
980
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Think all has been covered already, but echo-ing the above if I was getting my DB swapped and had a 3 phase head, I would put a little TPN board...
Replies
5
Views
389
  • Question
Why not fit a self contained SPD fed directly from the Henley blocks, and free up a bay? Could probably make one up from whats there, using a...
2 3 4
Replies
47
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top