Chr!s
-
Hi all,
Where do I get phase (Z1) and earth (Z2) conductor impedances to calculate earth fault loop impedance?
I have seen (R1 + R2) tables which give combinations for cable sizes up to 35 mm2. What about cables > 35 mm2?
Can I use voltage drop tables (for phase conductors) from Appendix 4 in BS 7671? These are impedance of the entire circuit though aren't though (in the case of single phase ccts includes phase and neutral conductors - so divide by 2?)?
Thats perfectly fine, divide by 1.73 for three phase assuming balance loads.
I want to calculate earth loop impedance for any size phase and earth conductors. Where do I get the impedance data from the Standards?
Apendix four or manufactures data
Thanks,
Battler.
Regards Chris