D

daiplayer

Any explanations on how this is calculated ?

Diversity :

By referin to table 1b in the osg, it states : 100% largest motor ?? ...3kw ....???

3000/230 = 13.04 A....is this it !!?? max demand ??


How there on would you make cable selection , mcb selection ?
 
once design current is established select a protective device (in) rated equal or greater to ib then select a cable rated equal or greater than in
 
Is it going to be run in armoured cable or twin and earth?, is the circuit a radial? A standard ring with 2.5mm t+e will take anything up-to 3kw on a 32A breaker and a radial on a 20A breaker.
Check your table in BS7671 for voltage drop per milliamp per metre, is the cable being clipped direct or going through thermal insulation, blah blah blah.
 
Is it going to be run in armoured cable or twin and earth?, is the circuit a radial? A standard ring with 2.5mm t+e will take anything up-to 3kw on a 32A breaker and a radial on a 20A breaker.
Check your table in BS7671 for voltage drop per milliamp per metre, is the cable being clipped direct or going through thermal insulation, blah blah blah.

I think that an A3 radial 2.5mm cable within a max floor area of 50m2 can take upto 5kW and be protected by a 20A breaker.

I think thats right.......
Sav
 
I wouldn't, The max I would put on a radial is 3KW, ie: immersion heater 16A or 20A breaker with a 20A double pole switch. Any higher I would go 4mm or 6mm cable 32A breaker. Just to air on the side of safety.
 
I think that an A3 radial 2.5mm cable within a max floor area of 50m2 can take upto 5kW and be protected by a 20A breaker.

I think thats right.......
Sav
5kw >20A. thats a bit high for a 20A MCB. then there's volt drop to consider. 4mm and 32A minimum in my mind.
 
this is the drawing ive been given to design for my final practical exam. A 3 kw motor will be wired in. It will run from the cu to a dp switch via twin and earth in conduit ( 2.5m run) from the dp switch, then run in swa cable to motor , 500mm, then back through it all. Ive have to show how i calculated all the cable design, considering volt drop and diversity. ??? For some reason i come up with : volt drop ( approx 2v) ....for 1.5mm cable, And since the osg says a 1.5mm cable can carry 17.5 A (ref method b) table 6D1. ?????????????? surely im wrong !!!!!!
 
3kw load at 230v is just over 13a so nearest mcb would be a 16 so although a 1.5mm cable can handle it (going off basic info given) then your design would be correct although not ideal, but do they want exact or for your judgement, now providing all your calcs are correct and you can show how you have designed the circuit then all should be good.
 
this is the drawing ive been given to design for my final practical exam. A 3 kw motor will be wired in. It will run from the cu to a dp switch via twin and earth in conduit ( 2.5m run) from the dp switch, then run in swa cable to motor , 500mm, then back through it all. Ive have to show how i calculated all the cable design, considering volt drop and diversity. ??? For some reason i come up with : volt drop ( approx 2v) ....for 1.5mm cable, And since the osg says a 1.5mm cable can carry 17.5 A (ref method b) table 6D1. ?????????????? surely im wrong !!!!!!

No your not wrong.
3kW motor.
Diversity= 100%. So 13A
Volt drop= mV/a/m (in osg) x 13 x 2.5m/ 1000.
So 1.5 is ok as a minimum but not the best. You would be better off on 2.5mm but I'm saying that out of instinct so I'm sure some would say you can get away with 1.5mm
 
I.5mm would be ok if you had a 2inch run of cable from the CU, if the run of cable is two floors away in a 5 bed house, I think you would be in trouble.
 
this is the drawing ive been given to design for my final practical exam. A 3 kw motor will be wired in. It will run from the cu to a dp switch via twin and earth in conduit ( 2.5m run) from the dp switch, then run in swa cable to motor , 500mm, then back through it all. Ive have to show how i calculated all the cable design, considering volt drop and diversity. ??? For some reason i come up with : volt drop ( approx 2v) ....for 1.5mm cable, And since the osg says a 1.5mm cable can carry 17.5 A (ref method b) table 6D1. ?????????????? surely im wrong !!!!!!

Are you sure that is right. I would have expected the question if it's a design one to want you to calculate the CPC sizing as well by using the adiabatic equation in reg 543.1.3.

So would it not be singles in that conduit?
 

Reply to Calculating volt drop, cable selection and mcb selection on an 3kw motor in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
912

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top