If your talking about load balancing over phases.....then....Yeah...kind of...but that would be in the inititial design of the heater itself......not considered during the heater installation...

Seeing as it a three phase supply...You consider that the load in q has already been balanced by the Maker of it.

Installers may need to consider balancing when installing single phase items...into a premesis that uses/ are provided by three phases...( ie,, three single phase (identical heaters) would be installed on a phase each ?


Correct me on this if im wrong though guys..
 
Ib = Power / SQUARE ROOT of three x Uo = 36.1 A

is that per phase?

The 36.1A figure is the design current for each line (L1, L2, L3) it is not a total value that is then shared between 3 cables if that is what you are asking:)

edit : you have to be a little careful with terminology because the phase current (Ip) only equals the line current (Il) when connected in star. If in delta, as it would most likely be in a motor, then Il = √3* Ip

When designing for cable size it is just the line current that you are interested in.

A complex subject (which i am rapidly forgetting:eek:) but just to be aware that phase current and line current are slightly different and are not always the same value.:)
 
Last edited by a moderator:
The 36.1A figure is the design current for each line (L1, L2, L3) it is not a total value that is then shared between 3 cables if that is what you are asking:)

edit : you have to be a little careful with terminology because the phase current (Ip) only equals the line current (Il) when connected in star. If in delta, as it would most likely be in a motor, then Il = √3* Ip

When designing for cable size it is just the line current that you are interested in.

A complex subject (which i am rapidly forgetting:eek:) but just to be aware that phase current and line current are slightly different and are not always the same value.:)

Much better explanation than mine...:)
 

Reply to Calculating volt drop, cable selection and mcb selection on an 3kw motor in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
919

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top