yes please mate. I could do with all the practise possible. Thankyou 

ok this is my findings :
Ib = 3000/230 = 13.04 A
Table 2A osg....pg100 bs3036 fuses : 15A ( In greater than Ib ) ?
Table 6E1 pg 131 osg, 1.5MM cable can carry 14A .....Correct cable selection ?????
Now heres where i get confused.....if this is correct : by apllying grouping factors...It (greater than or equal to) : In/Ca x Cg x Ci x Cc
SO... 15/1.03 x0.8 x 0.725 = 25.1 A ?????
Deos this mean i must therefore use 4mm cable ( table 6E1) ...??
And therefore use 4mm for volt drop ??? which should be done first ??
However for 1.5mm cable ....29x13.04x30 / 1000 = 11.34 v
????????????????????? lost ??????????????/ lol
thanks for the reply....Gettin the hang of it now i think. Wasnt aware of the heater load scenario though. LOL. Yeah any q's...(if u have the time would be great mate. Thankyou very much,
I regards to the earlier q....i take it that because the heater is 15m away from the supply....it not 30m ( line out 15m...neutral back) ?