Had a callout on Saturday. Customer had lost power in the night and now had a burning smell and a crackling sound from the "black lump at the top of the supply cable"
They'd called another company who quoted ÂŁ72 for a 30 min visit to investigate but couldn't say when in the day they could attend.
No other advice given.
The customers father knew me and was concerned so called me.
I told them over the phone it was likely a failure in the DNO feed or fuse and to turn off the CU main isolator till I got there. I also advised it was unlikely I could do much if it was before their meter.
When I arrived it was clear the DNO fuse had overheated. Cool by now.
Noted with customer that no seals present on the DNO fuse so I pulled it.
Incoming fuse holder blade socket was duscoloured and burnt. Fuse blade equally damaged.
Suspecting incoming cable screws loose I tightened and sure enough well loose.
It was clear a new fuse holder assembly needed and thats a DNO job.
Family had a baby in the house. So I cleaned up the fuse holder best I could and reversed the fuse holder and re-inserted.
Ensured no high current devices on. (Immersion kettle cooker shower) and re engaged supply.
Advised customer to only use lights and fridge freezer to keep load low and to monitor fuse for any issues.
At that point fuse holding ok.
Called DNO on their dangerous electrical fault line. Explained situation and requirement for priority callout as baby in house.
Left customer and heard from them a few hours later to say all sorted and ok now and no other cost to them beyond my callout fee that was much less than the ÂŁ72 they'd been quoted.

Anything different others here would have done?
If you'd had a spare DNO fuse holder would you have used that (socket badly damaged so of limited help)
 
The other tack to take would be to call splash and crash, due to the fire risk as it could be considered too dangerous / depending on proximity, to switch the CU off. I'm sure they'd get the DNO out pretty quick.
 
I will admit to laying it on a bit thick to the DNO when I called. I did say I didn't think it would catch fire but who knows...
 
Had a callout on Saturday. Customer had lost power in the night and now had a burning smell and a crackling sound from the "black lump at the top of the supply cable"
They'd called another company who quoted ÂŁ72 for a 30 min visit to investigate but couldn't say when in the day they could attend.
No other advice given.
The customers father knew me and was concerned so called me.
I told them over the phone it was likely a failure in the DNO feed or fuse and to turn off the CU main isolator till I got there. I also advised it was unlikely I could do much if it was before their meter.
When I arrived it was clear the DNO fuse had overheated. Cool by now.
Noted with customer that no seals present on the DNO fuse so I pulled it.
Incoming fuse holder blade socket was duscoloured and burnt. Fuse blade equally damaged.
Suspecting incoming cable screws loose I tightened and sure enough well loose.
It was clear a new fuse holder assembly needed and thats a DNO job.
Family had a baby in the house. So I cleaned up the fuse holder best I could and reversed the fuse holder and re-inserted.
Ensured no high current devices on. (Immersion kettle cooker shower) and re engaged supply.
Advised customer to only use lights and fridge freezer to keep load low and to monitor fuse for any issues.
At that point fuse holding ok.
Called DNO on their dangerous electrical fault line. Explained situation and requirement for priority callout as baby in house.
Left customer and heard from them a few hours later to say all sorted and ok now and no other cost to them beyond my callout fee that was much less than the ÂŁ72 they'd been quoted.

Anything different others here would have done?
If you'd had a spare DNO fuse holder would you have used that (socket badly damaged so of limited help)
IMO you went over and above, good for you, got the fault located and dealt with.
 
Had a callout on Saturday. Customer had lost power in the night and now had a burning smell and a crackling sound from the "black lump at the top of the supply cable"
They'd called another company who quoted ÂŁ72 for a 30 min visit to investigate but couldn't say when in the day they could attend.
No other advice given.
The customers father knew me and was concerned so called me.
I told them over the phone it was likely a failure in the DNO feed or fuse and to turn off the CU main isolator till I got there. I also advised it was unlikely I could do much if it was before their meter.
When I arrived it was clear the DNO fuse had overheated. Cool by now.
Noted with customer that no seals present on the DNO fuse so I pulled it.
Incoming fuse holder blade socket was duscoloured and burnt. Fuse blade equally damaged.
Suspecting incoming cable screws loose I tightened and sure enough well loose.
It was clear a new fuse holder assembly needed and thats a DNO job.
Family had a baby in the house. So I cleaned up the fuse holder best I could and reversed the fuse holder and re-inserted.
Ensured no high current devices on. (Immersion kettle cooker shower) and re engaged supply.
Advised customer to only use lights and fridge freezer to keep load low and to monitor fuse for any issues.
At that point fuse holding ok.
Called DNO on their dangerous electrical fault line. Explained situation and requirement for priority callout as baby in house.
Left customer and heard from them a few hours later to say all sorted and ok now and no other cost to them beyond my callout fee that was much less than the ÂŁ72 they'd been quoted.

Anything different others here would have done?
If you'd had a spare DNO fuse holder would you have used that (socket badly damaged so of limited help)
Spot on mate! Been to one similar a couple of years ago. Surprisingly working for the board, when doing cut out changes, it is amazing to find a 40 amp fuse present in the cut out.
 

Reply to Callout to arcing supplier fuse in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
385
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
966
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Our house in a row was built in 1971 and we have metric cables with cpcs for the lighting, top of the row imperial and no cpcs.
Replies
8
Views
2K
  • Question
This is a baffling fault I've been fighting with for a couple of weeks now, so I wondered if another set of eyes will help. I installed an EV...
Replies
0
Views
205

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top